Hi, I've read a couple of threads where the cold water supply ends up warm due to incorrect plumbing involving the desuperheater. I think my situation is a little different than the threads I've looked at. It would be helpful to get your expert advice and hopefully add another thread for future folks to help them in this situation.

The problem I have is that in the Florida summer, when the geo system is cooling, my cold water supply (e.g., to the kitchen sink) is warm. Also, the copper pipe supply to the desuperheater is warm to the touch. I don't have the problem in the winter.

I'm pretty sure the problem is that the cold water supply and the desuperheater supply are both drawing warm water from the buffer tank. I suspect that I need one more more check valves.

I've attached a simple sketch of the water softener, buffer tank, and T's to the desuperheater supply and cold water supply.  I have photos, but it looks like the maximum file size is 100Kb and I'm not sure how to get a photo down to that file size. 

What do I need to do in order to ensure the cold water and desuperheater supplies are not warm in the summer?

Thanks for all advice/guidance.



Attachment: Current_Layout_Sketch.pdf

newbostonconstUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:778

--
26 Jul 2024 04:37 PM
Is the other Desuperheater line to the geo unit coming off the buffer tank? Is the desuperheater line you have labeled the supply or the return?

I would swap the cold water to house and the desuperheater positions and put a check in between them.


"Never argue with an idiot. They will only bring you down to their level and beat you with experience." George Carlins
GreenBrykUser is Offline
New Member
New Member
Send Private Message
Posts:4

--
26 Jul 2024 05:33 PM
Yes, the other desuperheater line is connected to the bottom of the buffer tank. Thus, the hot water coming out of the desuperheater is fed to the bottom of the buffer tank.

The desuperheater line depicted on the diagram is the supply to the desuperheater. It is supposed to provide cool water to the desuperheater.

The copper pipe that is the depicted supply to desuperheater is warm to the touch, so it must be drawing water from the buffer tank. That's not good.

I agree that a check valve is needed. Wouldn't it be better to put it after the cold water supply line? That way, neither of the two lines before it could draw from the buffer tank.


newbostonconstUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:778

--
27 Jul 2024 05:01 PM
Water is circulated when ever the unit is running...I think it runs if you are heating or cooling...so when the tank starts getting warm you will have warm water at the inlet to the house cold water supply the way it is plumbed.

That is why I think you need the cold water before the desuperheater and a check between the two as I stated above.

A check in the cold will stop convection currents but when you are pulling cold water for the house and the unit is running you are going to get water that is the temp of the tank to your fixtures with your current setup. It was plumbed wrong from the start in my opinion...



"Never argue with an idiot. They will only bring you down to their level and beat you with experience." George Carlins
GreenBrykUser is Offline
New Member
New Member
Send Private Message
Posts:4

--
28 Jul 2024 12:37 PM
Thanks so much for your additional reply, newbostonconst. May I ask a follow-on question? If I switch the cold water and desuperheater supply line and put a check valve between them, won't the desuperheater supply line continue to have convection currents when the unit is running? (that supply line is warm to the touch when the unit is cooling). Would it make sense to add the check valve after both supply lines?

Again, thanks for the replies. I have the plumber coming out next week.


newbostonconstUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:778

--
30 Jul 2024 01:52 PM
One check is enough. convection currents are fine. Geo desuperheater is supposed to heat the water while heating or cooling. Desuperheater pump will overcome convection currents. If you are worried about the warm pipes then insulate them.

Good luck...


"Never argue with an idiot. They will only bring you down to their level and beat you with experience." George Carlins