Yonder
New Member
Posts:14
|
04 Nov 2014 08:02 AM |
|
I'm in the process of getting my geothermal heating all sorted out, and one thing that concerned me was the borehole separation. I have two 240' boreholes that were supposed to be 16' apart. When they moved the drill for the second hole they seemed a little close to me. I asked if they had measured it as 16' and they said yes, so I went about my business.
Once they were done I took my own measurements for my property plot and found that (center to center) the boreholes are only 14'5" across. Is that enough? Is 16' an overly generous buffer?
Edit: Just talked to the installer and he says that the real minimum is 10', and since they are farther apart than that it should be fine. |
|
|
|
|
|
jonr
Senior Member
Posts:5341
|
04 Nov 2014 09:23 AM |
|
You won't notice that minor difference (see purple line, figure 7). On the other hand, without space constraints, I'd use 25'. And I'd orient a 1x2 array perpendicular to ground water flow (can be worth ~5%). |
|
|
|
|
joe.ami
Veteran Member
Posts:4377
|
04 Nov 2014 10:26 AM |
|
It's fine.
|
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
Bill Neukranz
Veteran Member
Posts:1103
|
04 Nov 2014 11:48 AM |
|
Posted By jonr on 04 Nov 2014 09:23 AM You won't notice that minor difference (see purple line, figure 7). On the other hand, without space constraints, I'd use 25'. This is an exceptionally helpful document to read. Best attempt to quantify benefit of various borehole sizing's I've seen. Thanks. Bill |
|
Energy reduction & monitoring</br> American Energy Efficiencies, Inc - Dallas, TX <A href="http://www.americaneei.com"> (www.americaneei.com)</A></br> Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
|
|
|
fun2drive
New Member
Posts:68
|
04 Nov 2014 06:37 PM |
|
In this area it is 10 ft separation so I guess it all depends on the location and what us usual and customary. |
|
|
|
|
docjenser
Veteran Member
Posts:1400
|
08 Nov 2014 07:07 AM |
|
Assuming all factors being equal, and assuming average conductivity, load etc...The difference in performance between 2 boreholes 14.5 ft apart versus 16 ft apart is about 0.5F at the peak of the heating season, meaning if your system is designed for 30.5 F with 16feet apart, with 14.5 ft apart it will drop down to 30F. I don't know your loads, but given that you posted before that you have a 3 ton heatpump, the average loop temp will only be affected by a tiny amount. The difference in annual operating costs are less than $2. |
|
www.buffalogeothermalheating.com |
|
|
Palace Geothermal
Veteran Member
Posts:1609
|
08 Nov 2014 10:12 AM |
|
since drilled holes never go straight down, it is possible for two holes to intersect under ground. This is reason enough to keep distance. We shoot for at least 15', most commercial jobs go for 25' |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
robinnc
Advanced Member
Posts:586
|
08 Nov 2014 07:24 PM |
|
They don't go straight down? I've never heard of that before.
|
|
|
|
|
Yonder
New Member
Posts:14
|
09 Nov 2014 03:55 AM |
|
That didn't occur to me before, but it makes sense. Steel isn't particularly rigid when you've got a 200 foot column of it that's only 6-8 inches wide, especially when you are pushing on it. It'd be interesting to point a laser range finder down a new hole and see how far down it went before it started to stray. |
|
|
|
|
Palace Geothermal
Veteran Member
Posts:1609
|
09 Nov 2014 10:05 AM |
|
I have seen a loop 25' away get drilled into . ... here is what you might see |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
Yonder
New Member
Posts:14
|
09 Nov 2014 11:13 AM |
|
Wow, how deep do you have to go to get that amount of wandering? |
|
|
|
|
docjenser
Veteran Member
Posts:1400
|
09 Nov 2014 04:18 PM |
|
Yep I have seen it too. |
|
www.buffalogeothermalheating.com |
|
|
Palace Geothermal
Veteran Member
Posts:1609
|
09 Nov 2014 07:05 PM |
|
if the drilling is in an area of large bolders, the drill bit can wander off plumb when glancing of the side of a boulder. Kind of like a ricochet. The holes were 300' deep where this happened. |
|
Dewayne Dean <br>www.PalaceGeothermal.com<br>Why settle for 90% when you can have 400%<br>We heat and cool with dirt!<br>visit- http://welserver.com/WEL0114/- to see my system |
|
|
joe.ami
Veteran Member
Posts:4377
|
10 Nov 2014 08:59 AM |
|
Doc points out the more practical side. The consequence is a fraction of a percent of the annual operating cost. |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
jonr
Senior Member
Posts:5341
|
10 Nov 2014 09:41 AM |
|
The consequence is a fraction of a percent of the annual operating cost. Unless a hole isn't straight and the spacings of 14.5' and 16' feet at the surface become something like 1.5' and 3' below the surface. Unlikely, but that would make more like a 7% difference - with the overall loss (compared to straight @ 25') going from ~18% to 25%. Use three or more boreholes and spacing becomes even more important. Unfortunately, it's unlikely one can get a thermal performance guarantee beyond "it works" - so I guess the owner should watch for and investigate corner cutting. But in this case, let it go. |
|
|
|
|
joe.ami
Veteran Member
Posts:4377
|
10 Nov 2014 10:36 AM |
|
"Unless a hole isn't straight and the spacings of 14.5' and 16' feet at the surface become something like 1.5' and 3' below the surface." To the question does 14.5' instead of 16' spacing matter the answer "The consequence is a fraction of a percent of the annual operating cost." is correct. IF the bores aren't straight, IF the bores aren't grouted, IF the header pipe is kinked, IF the bores are too short, IF the bores weren't correctly flushed...........IF........... Yes many things could be wrong that matter, but the lost 1.5' of spacing isn't one of them and hopefully we can put that concern to rest for a consumer who just spent alot of money vs worry about the boogeyman in the closet. |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
docjenser
Veteran Member
Posts:1400
|
10 Nov 2014 03:19 PM |
|
Posted By jonr on 10 Nov 2014 09:41 AM
The consequence is a fraction of a percent of the annual operating cost. Unless a hole isn't straight and the spacings of 14.5' and 16' feet at the surface become something like 1.5' and 3' below the surface. Unlikely, but that would make more like a 7% difference - with the overall loss (compared to straight @ 25') going from ~18% to 25%. Use three or more boreholes and spacing becomes even more important. Unfortunately, it's unlikely one can get a thermal performance guarantee beyond "it works" - so I guess the owner should watch for and investigate corner cutting. But in this case, let it go.
1.5 foot is far away from corner cutting. No reason to assume that there is anything wrong. He should enjoy the geosystem! Jon, please enlighten me, why is the overall loss between 18-25% if the distance becomes 1.5' - 3' below the surface? |
|
www.buffalogeothermalheating.com |
|
|
Yonder
New Member
Posts:14
|
10 Nov 2014 03:44 PM |
|
At that distance your two holes will transfer to the same part of the ground. I'd expect you to over-saturate the ground, so that shortly in to each season the water temperature would get quite cold/hot for winter and summer respectively, so your unit would have to work very hard to keep moving the heat against the gradient. In the winter you'd probably end up using Aux Heat a lot as well. |
|
|
|
|
docjenser
Veteran Member
Posts:1400
|
10 Nov 2014 05:57 PM |
|
Posted By Yonder on 10 Nov 2014 03:44 PM
At that distance your two holes will transfer to the same part of the ground. I'd expect you to over-saturate the ground, so that shortly in to each season the water temperature would get quite cold/hot for winter and summer respectively, so your unit would have to work very hard to keep moving the heat against the gradient. In the winter you'd probably end up using Aux Heat a lot as well.
I understand the principles of heat transfer!
Just to clarify, are we talking about missing 1.5-3' from the 16 feet, or about the 2 loops only being 1.5-3' apart. If it is the latter, the loss is performance is a bit more than 18-25%. Thus the question how John came up with that number. |
|
www.buffalogeothermalheating.com |
|
|
Yonder
New Member
Posts:14
|
10 Nov 2014 06:02 PM |
|
Ah sorry, I read him as saying that eventually the boreholes came within 3' of each other, and I assumed that his percentage was based off of an assumption of when the boreholes would get that close together. I would imagine that the boreholes would remain 15' away for at least a hundred feet before starting to wander off near each other, and they would probably approach each other fairly gradually. |
|
|
|
|
joe.ami
Veteran Member
Posts:4377
|
11 Nov 2014 08:28 AM |
|
Even if the seperation of the tails was 1.5 to 3' at the end of the vertical loops, the average seperation would be much greater. i.e. we start 16' apart and end at 3' average distance will likely be at least 6.5' and likely greater as the path isn't likely truley diagonal , it is more likely paralell with the occasional jog. Also depending on the number of loops there may be benefit elsewhere due to greater seperation from other loops. I think the estimation of 18-25% impact is high. |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
docjenser
Veteran Member
Posts:1400
|
11 Nov 2014 09:39 AM |
|
Posted By Yonder on 10 Nov 2014 06:02 PM
Ah sorry, I read him as saying that eventually the boreholes came within 3' of each other, and I assumed that his percentage was based off of an assumption of when the boreholes would get that close together. I would imagine that the boreholes would remain 15' away for at least a hundred feet before starting to wander off near each other, and they would probably approach each other fairly gradually.
For the purpose of this discussion, your loop field should be fine, the 14.5' instead of 16' distance has no significant impact on your performance. |
|
www.buffalogeothermalheating.com |
|
|
jonr
Senior Member
Posts:5341
|
11 Nov 2014 10:45 AM |
|
As I said, "unlikely" - consider my numbers (based on a double jog) a near worse case example serving only to illustrate that "fraction of a percent" isn't always correct when you only know surface distance. On the other hand, as geodean's picture shows, unlikely, worse-case events can happen and it's often good to know what they are.
With two holes, deviation from straight is just as likely to improve performance. So the typical/likely case = 0% impact. I'm pretty sure that Yonder has moved from concerned to interested in the theories. The numbers are straight from the graph in the reference. |
|
|
|
|
Yonder
New Member
Posts:14
|
11 Nov 2014 11:43 AM |
|
Oh yeah, sorry, my concerns on the 14'5" separation between the boreholes have been alleviated. I'm still annoyed that they drillers didn't do it to spec, but I'm not concerned about the capability of my unit (although I will be tracking my incoming water temp to look for signs of oversaturation, it looks like I'm fine as long as incoming water temperature stays above 30 F from discussions I've seen skipping around this forum). My last posts were just out of interest of the intersecting boreholes. |
|
|
|
|
docjenser
Veteran Member
Posts:1400
|
12 Nov 2014 01:58 AM |
|
Posted By jonr on 11 Nov 2014 10:45 AM
As I said, "unlikely" - consider my numbers (based on a double jog) a near worse case example serving only to illustrate that "fraction of a percent" isn't always correct when you only know surface distance. On the other hand, as geodean's picture shows, unlikely, worse-case events can happen and it's often good to know what they are.
With two holes, deviation from straight is just as likely to improve performance. Ie, typical/likely case = 0% impact. I'm pretty sure that Yonder has moved from concerned to interested in the theories. The numbers are straight from the graph in the reference.
Now keep in mind that the numbers, formulas and algorithms the tables and software programs are using are derived from certain field measures. How did people know that the pipes did not deviated from straight when they originally established those performance numbers? |
|
www.buffalogeothermalheating.com |
|
|