Slab reinforcement
Last Post 22 Oct 2008 07:30 AM by wes. 2 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
TavameUser is Offline
New Member
New Member
Send Private Message
Posts:5

--
21 Oct 2008 04:51 PM
Should I be using steel reinforcement in my 4" basement slab?

We will have 4000 psi concrete with fibermesh in it, and radiant tubing installed on foam insulation using screw clips. But i have read so many conflicting ideas about rebar, that I'm confused.

ACI recommends that unreinforced slabs have control joints. Reinforced slabs with wider spacing control joints (non-structural) use the rebar to limit crack separation, and to use rebar a minimum 14" o.c. so that crew can walk around and not disturb the rebar while placing concrete. Wiremesh can be used but you have to be extremely careful that it is installed at the top 1/3 of the slab to help with crack control. Having seen how flatwork and concrete is placed, I would think it would be impossible to keep the wire fabric at the proper height for it to do what it is intended to do.

So my question is, should I use rebar at 16" o.c. with control joints ever 10' (the cost is significant for 2000 ft^2 slab), or should I do unreinforced slab with closer control joints? I will greatly accept any advice.

Thank you.


AltonUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2164

--
21 Oct 2008 05:50 PM

In my opinion, wire mesh is not worth the effort, especially in a basement slab.  Fibermesh is ok but you will see it unless the floor has some type of covering over it.  I see no reason to use rebar in the floor slab unless it is needed to protect against loose fill, expansive soils or earthquakes.  Maybe other people will give you their opinions also so you will have some choice.  If all else fails, talk to your local code official.  They have a lot of experience in their regions.

Residential Designer &
Construction Technology Consultant -- E-mail: Alton at Auburn dot Edu Use email format with @ and period .
334 826-3979
wesUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:810

--
22 Oct 2008 07:30 AM
I agree with Alton, if you don't mind your slab being fuzzy, the fibermesh should be sufficient for general basement use.
If you have a garage area you might reinforce that. Watch your control joints with your radiant tubing.
Wes Shelby<br>Design Systems Group<br>Murray KY<br>[email protected]