Dana1
Thx for the detailed reply. The good news is assuming I follow you correctly we do indeed attach the XPS directly to the foundation and the 2x4 wall is built interior to that thereby keeping the "wood completely on the warm/side of the insulation". This of course leaves a cavity for HVAC supplys and the optionality to add additional FG insulation if desired or in this case the face of the 2x4 wall will be what the nailing fins of the shower surround will attached to.
My specific question is when I have XPS
attached directly to the foundation wall and sealed on all 4 corners (this gets me my airbarrier) and a 2x4 wall interior to that, in which a tub/shower surround is attached. You basically have 3 options before you attach the surround to the studs:
1# Fill the cavity with FG insulation as suggested by the article below: "Unfaced fiberglass batts can be installed in the frame wall for additional insulation. These details are shown in Figure 1. Closed cell sill seal should be installed between the bottom plate of the wall and the concrete floor"
This is typically how we approach retrofit situationshttp://www.buildingscience.com/documents/reports/rr-0308-renovating-your-basment(photograph 1 is my exact configuration. I attach the surround to the studs)
#2 Put nothing in the 2x4 cavity as the 2'' of XPS attached to the foundation suffices. And simply attach the surround to the 2x4 framed wall which again is interior the XPS
#3 Add a layer of EPS over the 2'XPS 's ( which I assume to be your preference due to increased permability which will establish a higher R-Value)
Or does the 2'' of XPS on the wall suffice?
The main question here is behind these type of surrounds (prone to more vapor diffusion ) if additional insulation beyond the 2'' of XPS attached to wall is necessary.
I assume any tub/shower surround is highly
impermeable.
Thanks
Matt