Unvented Roofs
Last Post 04 Jan 2010 11:03 AM by Bob I. 10 Replies.
11 Dec 2009 06:04 AM
Came across this paper listing the advantages of unvented roof assemblies..... courtesy LaGrange Consulting
Attachment: General_Notes_About_Unvented_Attics.pdf
greentreeUser is Offline
11 Dec 2009 07:14 AM
It should be noted that the document is specifically for hot humid climates.
BuntlyUser is Offline
11 Dec 2009 01:38 PM
I realize there are some advantages to an unvented attic. I am currently doing a ranch home that is a 40x60 box with an 8/12 pitch gable roof. By doing a vented attic there is only 2400 sq feet of conditioned space exposed the the outside. If I were to do an unvented attic, there would be approx 2884 sq feet of contitioned space exposed to the outside temps. From a heatloss/gain standpoint, I don't see how an unvented attic would be a benefit.
Bunt
Bunt
11 Dec 2009 03:08 PM
Posted By Buntly on 12/11/2009 1:38 PM
Bunt
Because heat loss is more than just R-value.  It's far easier to get the infiltration factor down to ZERO on an unvented attic, so you can punch in lighting cans, plumbing, ducts, whatever into the ceilings of the rooms below with great abandon, and you needn't worry about maintaining a tight air seal on the attic door/hatch, whatever.  The performance lost by the increased area is usually more than offset by the boost in air tightness. (Of course there will be many exceptions to prove the rule...)
Labor-wise air-sealing the attic floor to perfection can be substantial- far more than the labor for foaming the underside of a roof deck.  The increase in total (not just roof) exterior area for the structure is under 3%, and far LESS than the glazed area gain/loss factors in most homes.
Beyond heat gain/loss it means whatever gets stored/installed in the attic is within the pressure, thermal & hygric boundary of the envelope.
Also 8/12 is a much steeper pitch than most ranch homes, and of course, the higher the pitch, the greater the difference in exterior surface area.  In non-snow-zones in the US  most ranch homes have pitches under 5/12, with a correspondingly lower difference in attic-floor vs. roof deck + gable area.
11 Dec 2009 03:54 PM
as greentree stated it was for hot humid climates, if you were in a northern climate it may not be to your benefit, however I never could understand the reasoning of running warm ducts thru a cold basement or cold ducts thru a hot attic?
12 Dec 2009 08:59 AM
I dont understand ducts through an attic either, however most people condition their basements and use them for living space, so your warm ducts are in your warm basement.
16 Dec 2009 06:25 AM
How about cold climates?
16 Dec 2009 12:27 PM
Posted By greentree on 12/12/2009 8:59 AM
I dont understand ducts through an attic either, however most people condition their basements and [b]use them for living space, so your warm ducts are in your warm basement.[/b][/quote]
A whole lot o' housing in the southern US (particularly in swampy low-lying area of FL, MI, and LA) are built slab on grade, since basements would have to be shallow, pumped out often, and nice homes for pesky critters.
And the ducts, being used primarily for AC, are less than optimally places in a fully vented attic.
That's not to say it isn't also a good idea in HEATING dominated climates without ducts in the attic- it IS.  It's a reliable way of achieving near-perfect air sealing as compared to the detail, and likelihood of deterioration/damage you get at the attic-floor/conditioned space ceiling level.  The number and size of ceiling penetrations on the conditioned spaces are often large (especially amongst recessed lighting enthusiasts), then there's leakage at the tops of stud bays, etc. etc.  Infiltration is often 30-40% of the heat loss in a house, and the most critical points to seal to slow down the flow are at the top (attic) and the bottom (foundation sill), which is where the stack pressure issues are highest.
CaseyRUser is Offline
02 Jan 2010 05:28 PM
I was about to start a thread, but will hi-jack this one instead...
I am planning on closing off the way-to-small vents in my attic and including it into the conditioned space.  My house is in the S.F. Bay area within sight of the Bay and thus no worry about freezing and no summer temperatures for more than a week each year (Bay Area residents melt at anything over 80 degrees F....)
The house is a small 1960 vintage Calif. ranch with 2:12 roof pitch and with what I guess would be called a cathedral ceiling at each end.  Between the bedrooms at one end and the living room at the other is the attic area which covers about 25% of the house, over the hallway and the bathrooms.  There are a total of three vents at the eves with a total vent area of 1/3 of a square foot - just enough to let the winter winds drive out some of the heat and which appear to provide no ventilation during the one week of the year when temps are 80 degrees or higher.
The heating ducts are in this area and there is no insulation on the 2 foot sections of the upper wall shared with one bedroom and the kitchen.  The roof is an unusual construction composed of what was originally called "Hemasote" panels which are fiber panels about 3.5" thick with an R value of about 2 per inch.  I had two inches of polyiso placed on the roof when I had the hot mopped roof replaced several years ago, so the roof insulation R value would be on the order of 18 or so.
With that background, my question: what is the proper way to include the area into the heating envelope area of the main house.  When I close off the small outside vents, do I need to vent the area into the main area of the house - perhaps one of the bedroom closets and/or the living room or kitchen.  If so, does anyone have any idea of how large the vents should be?
I was thinking of just cutting a vent into the access hatch in one of the bedrooms and having it the same size as the previous external vents.  Would vents at each end provide some advantage?
Thanks, Casey
Whoops, not quite familiar with the mechanics of the form, this is not a response to greentree...
02 Jan 2010 07:04 PM
Casey;
plug up the exterior vents and if possible a little plug of insulation at the open end between rafter tails , if accessable?
opening a vent from the current conditioned space will serve no purpose, once you seal of exterior that void will become close to the same temperature as your living space, without cutting any holes
Bob IUser is Offline
Casey
you already have an insulated roof; the attic vents simply short circuits the roof insulation by introducing outside air into the attic. So yes, close up the vent areas. BTW, Homosote Corp is still in business if you have questions about the product.