Posted By egouin on 01/17/2010 9:54 PM
I like your thinking, but I would have concerns about the flammability of the materials (never researched it, just a thought).
In the stick built areas of my house, I used either 1/2" or 1" rigid foil faced foam between the studs and the drywall. Did the same for the ceiling of the under house garage.
I recently had a chance to check my house with a thermal imaging camera. Attached is a thermal image of one of those walls. The only thing you can see (colder) on these walls are the screw heads (and the window of course). Neat.
Good luck,
Ed
Sill gasket is flammable, but 1/2" of gypsum board is deemed an adequate thermal barrier for fire safety for such materials in the IBC. By virtue of it's being under the wallboard, it's safe.
The effect on thermal bridging is very slight with then materials like sill gasket. Closed-cell foams of that ilk run about R6 per inch of thickness, but when you're talking only 1/8" (less, when compressed), figure on getting about R0.5 out of it, best-case.
As for acoustic isolation with sill gasket, it won't buy you much- it'll be measurable with instrumentation, but not so noticable with your ear. Double layering of the gypsum, glued together with
acoustic dampening adhesive buys you much more. Blowing cellulose into the cavity to a density of at least 3lbs/ft^3 will also have a large effect- far more than standard density fiberglass batting, and more than lower density 2-hole method blown fiber.
Acoustiblok/Thermablok strips between the studs and gypsum will give you both significant acoustic isolation AND thermal break (at similar cost to double gypsum, IIRC).