Dana, that looks to the best solution for my situation. The domestic hot water is supplied through an embedded coil, so it is a candidate for an Ergomax type system. What is the ballpark cost of that unit? The intellicon seems very reasonably priced, but would not make my system any more efficient at supplying dhw.
A ~30 gallon ErgoMax (or Turbomax) runs about a grand + shipping.
A ~50 gallon version runs more. The Everhot EA series is also worth
considering. Anything over 25 gallons will work. The amount of hot
water flow you can get out of the thing is a function of the tank size, storage temp, the boiler's output and the size of the heat exchanger. If
it's serving 3 bathrooms @5gpm each for 15+ minutes at a time you may need to bump up one or more factors. But it'll crank considerably more hot water than any internal coil on a boiler.
To keep flue-condensation from becoming an issue, set the tank no lower than 140F, but set up the controls for cold-starting the boiler for cold start rather than maintaining a standby temp. You'll need a mixing valve/tempering valve on the output to reduce the output temps to non-scald levels (but that's probably true in your current installation.)
Which model WGO is it? The 2-plate version might have issues running 3 showers and a the heating load simultaeously but the -03 & -04 would give you some margin.
The Ergomax has separate heating & boiler ports built into the tank, making plumbing it for hydraulic separation, but with the TurboMax & Everhot EA you'll need to use Tees.
The topology you want is:

(It doesn't have to be an ECM circulator & valves, it could be separate circulators for the different zones with check valves.)
The Tees would essentially be narrwings at the top bottom of the tank, with the boiler output Teed with the radiation supply, and the boiler return Teed with the radiation return.
The boiler control is then slaved to the tank's aquastat as it's only zone, and heating zone thermostat calls control the radiation circulators or zone valves. The boiler remains agnostic about the the state of the heating zone calls, only responds to drops in tank temp. The flow on the boiler loop needs to be high enough to keep the delta-T across the boiler under 25-30F, but neither the head of the boiler nor the head of the tank is very high, you might think about using a 3-speed circulator on the boiler loop if you can't come up with the actual head & flow numbers in your design. If the delta-T across the boiler is under 15F you can probably save a bit of electricity running the pump slower.
The radiation will run at about the tank's setpoint, not the boiler's output temp. The lower the temp, the higher the efficiency (figure on ~3% fuel savings for every 10F you can drop the temp.) But below 140F you run into condensation hazard conditions. If the flue has a stainless liner and a condensate drain/disposal you can get away with running cooler, but under no circumstances should you run it as low as 130F unless you plumb in a separate "boiler bypass" to keep the water entering the boiler at 140F or above. At 130F input water you can damage the heat exchangers of the boiler with condensation.
A cheaper alternative would be to use a standard indirect plumbed as a separate zone, and letting the boiler cold-start, but that wouldn't lengthen the burns on the heating calls from the smaller zones, which reduces operating efficiency below what it would be with a "reverse indirect" plumbed as a buffer/hydraulic separator.