30 year old 2000 sq ft. rancher in PNW
Last Post 29 Oct 2010 11:23 AM by Dana1. 7 Replies.
|
Sort:
|
|
Prev Next |
You are not authorized to post a reply. |
|
Daler
 New Member
 Posts:10
 |
| 23 Oct 2010 08:19 PM |
|
30 year old 2000 sq ft. rancher in PNW :
Looking to close off our crawl space vents to outside and make the area more conditioned. The 3' CS is all concrete, including floors (vapour barrier under). Insulation in subfloor joists.
I will need some sort of air circulation to replace the open vents and was thinking of tapping into the HRV supply trunk and running a small vent to the CS, and perhaps also putting in a small exhaust fan at one of the existing and opposing CS vents.
The HRV unit is situated in the garage and the insulated mechanical ducts are run throughout the long attic. All living space 4" vents (fresh air & exhaust) are in the ceiling.
What is your opinion on how I can best do this without screwing up the HRV application, and perhaps potentially contaminating the living space above?
Also, what minimum size of duct would be needed to move some of that supply air into the CS? The HRV is currently balanced and can that be maintained? |
|
|
|
|
|
|
Dana1
 Senior Member
 Posts:6991
 |
| 25 Oct 2010 05:09 PM |
|
The general solutions aren't much different than in other climate zones, except that in the PNW your outdoor dew points are lower, so condensation issues in a crawl space is even less likely than in this thread: http://www.greenbuildingtalk.com/Forums/tabid/53/aff/14/aft/77769/afv/topic/Default.aspx See also: http://www.buildingscience.com/documents/insights/bsi-009-new-light-in-crawlspaces http://www.buildingscience.com/documents/information-sheets/5-thermal-control/crawlspace-insulation/files/bscinfo_512_crawlspace_edit.pdf Once you've insulated the walls and rim joist and put vapor-sealed the floor, the ventilation requirements for the crawlspace fall to nearly-nothing, and it won't be growing mold or leaking soil-gases into the house, and circulating that air with conditioned-space air is the right approach to keeping it from stagnating. A couple of floor grills in out of the way places and a very modest amount of ventilation air circulating in from conditioned space works. One suggestion I've read was to locate one of the grilles in the laundry room near or under the clothes-dryer an the other in a hall or closet floor on the opposite side of the house, utilizing the pressure differential generated by the dryer's exhaust for a minimal air exchange. That's not as reliable as a bathroom-fan on an interval timer driving the loop though. Think 1-2 air-exchanges per-DAY, rather than per HOUR. The ventilation requirements are nowhere near what you'd need for conditioned space, as long as there are no combustion appliances in the crawl. Un-balancing your HRV to tap a small stream of air in there is silly. Depending on WHERE in the PNW you are, it may also make sense to add ~ R5-R10 of EPS foam insulation on the floor of the crawlspace, not just the walls (depends on your local subsoil temps. If it's below ~50F/10C, consider it.) If you insulate the crawlspace floor it's good to add a thin "rat slab" of 1.5-2" thickness over it as both an ignition barrier for the foam, and to protect the foam from crawling/walking damage when working there. The slab is non-structural, none too critical. You could also use half-inch OSB and still meet code on ignition barrier. |
|
|
|
|
Daler
 New Member
 Posts:10
 |
| 25 Oct 2010 08:19 PM |
|
I live in Victoria, BC I've read most all of the lit relating from Building Science to crawl spaces (CS) -- thanks. I notice their latest article is fascinating as it expands their survey of residential apps -- http://www.advancedenergy.org/buildings/knowledge_library/crawl_spaces/pdfs/Closed%20Crawl%20Spaces.pdf After we addressed some perimeter drainage and irrigation position problems (and turned out downspouts out into the garden) we now have a more stable CS RH. The next step we are planning is to completely fill the subfloor joist cavities with fg batt insulation including the floor joist end pockets. Spray foam is out of the question for us as it is cost prohibitive in these parts and we've also ruled out insulating the CS foundation walls as, according to different studies it will make little difference in our situation/climate (ie, see above BuildingScience article). The CS floor is already vapour proofed with 2" of parged cement sprayed over 6 mil poly that is attached to the footings at the base of the concete foundation. Incidentally, the CS is 2300 sq ft and averages 42" high. With the minimal amount of fg insulation we took down from the floor joists (in order to seal all floor penetrations) the RH has climbed back up to 68%. I think the higher RH may be moving up due to the warmth convecting through the floor from the above conditioned area ..and maybe the rainy season upon us now. Dispite some opinions, we would rather not directly connect our CS to the living area through any sort of passive floor venting. No matter how meticulous we are with sealing the CS there are still areas where RH builds up. Our main concern now is to devise a way to circulate that "bad" air that will eventually route it outside. As it is right now our HRV appears to be slightly negatively balanced and it may be drawing stuff up from the CS -- when we turn the HRV off, we are feeling much better! Besides chasing down opinions on tapping into our HRV, other ideas have been to open or increase the air venting, or just adding a small ventilator such as this: http://www.tjernlund.com/retail/underaire.htm , and replace that exhausted air with makeup air from a partially closed vent at the opposite end of the CS. The CS would still be segregated from the living area but would have its own air movement. Do you these sound like viable options? So far as that HRV idea goes, I had figured that since we have an oversized HRV for the main living area, why not take off a couple of ducts : the fresh air supply and the stale air return, and introduce them to opposite ends of the CS. So I got to thinking (and perhaps with your input above) that that may not be such a good idea after all -- the colder stale return air from the CS will end up mixing with that from the living space (at the HRV) and will probably drop the exchange efficiency of the handler quite a lot, especially in very cold weather. Also, that may lead to a problem of maintaining some sort of reasonable balance of the HRV system. Of course, when the HRV is off (as in summer), the HRV local vents may convect as they are tied together along the main plenum. This condition could then contaminate the living space air with that from the CS. Hmm.. how about just introducing only one duct with the fresh air supply from the HRV, then having a small vent in the CS for makeup air thus keeping it from pressurizing -- would this work? Perhaps a semi-conditioned space is all that we will require ..a sawed-off-basement heatsink is not what we need. Now if I can only decide on the best ventilation course of action before continuing with our expense and hassle..
|
|
|
|
|
Dana1
 Senior Member
 Posts:6991
 |
| 27 Oct 2010 01:08 PM |
|
Running the crawlspace warmer without the insulation between the first floor & crawl REDUCES the relative humidity of the crawl space rather than increases it. But sealing all of the air penetrations to conditioned space likely reduced a drying path for moisture getting into the crawlspace through the concrete walls and air-leaks through the foundation sill & band joist. (Those air leaks will be somewhat drier during the winter- the fall/spring warmer rainy periods are typically your worst case conditions in your area.) 68% RH is too high- you WILL get mold conditions on the joist edges (which is probably creating the "bad" air down there). Running the crawl space cooler with more fiberglass between the joists will only make it worse. A single 200-300 board-foot DIY kit for 2lb foam would be suffient material for air-sealing foundation sill and band joist to ~R6 (1" thickness). Then, sealing the interior face of the concrete with a vapor-permeable silane-based sealer will reduce the flow of ground & rain moisture through the foundation slightly, then putting even an inch (R5) of XPS on the concrete, foundation sill, and rim joist will lower the RH of the crawl space by two mechanisms: The XPS is only semi-permeable to water vapor, and insulating the foundation will raise the average temp of the crawl space. A combination of 1" of XPS + a mini-studwall with R11-13 UNFACED rock wool or fiberglass batting (and no interior-side vapor barrier) would be nearly ideal for Victoria's maritime climate. (Great city, BTW- I love the summers there!) I'm not sure if the nat'l builing code has recognized yet that inerior vapor retarders are far more likely to create than prevent problems in coastal BC- you might have an argument with the code inspector on that one, in which case using 3-4" of unfaced EPS instead of 1" XPS (without insulation in the studwall) would put you in the same R-range and is it's own barrier. With it vapor sealed at the floor, vapor-retarded and air-sealed at the foundation wall, and kept warm enough the the RH stays well above the mold range on the joists, there simply IS no contamination issues by mixing conditioned & crawlspace air. As for the Advance Energy research summary you linked to , your nowhere NEAR as cold in winter as places like Flagstaff, but you're also nowhere near as DRY, and they didn't insulate the CRAWLSPACE floors, only the crawlspace walls. In all cases the crawlspace stayed much drier with insulated walls rather than insulated floor. In Victoria the subsoil temps are ~10C, and if you insulate the walls of the crawlspace to ~ R10-R20 and the crawlspace floor to ~R8-10 you'd have the best of all worlds. If you insulated the above space floor to R20 between the joists the crawlspace will run colder and more humid. If you go with the latter putting at least half the R value below the joists and air tight (with say, 2-3" of unfaced EPS rigid board, for lowest cost) will keep the joist edges well out of mold/rot danger, and the crawl could be vented to the outdoors. Then again, if the same EPS were laid atop your cement-parge crawlspace floor and insulated the foundation walls you'd be in about the same place, with less labor, and have a warmer-dryer crawlspace. (R8 of EPS will run you about the same money as R5 in XPS, but it'll be twice as thick- you have some headroom to work with.)
|
|
|
|
|
Daler
 New Member
 Posts:10
 |
| 28 Oct 2010 12:36 PM |
|
Posted By Dana1 on 27 Oct 2010 01:08 PM Running the crawlspace warmer without the insulation between the first floor & crawl REDUCES the relative humidity of the crawl space rather than increases it. But sealing all of the air penetrations to conditioned space likely reduced a drying path for moisture getting into the crawlspace through the concrete walls and air-leaks through the foundation sill & band joist. (Those air leaks will be somewhat drier during the winter- the fall/spring warmer rainy periods are typically your worst case conditions in your area.)
68% RH is too high- you WILL get mold conditions on the joist edges (which is probably creating the "bad" air down there). Running the crawl space cooler with more fiberglass between the joists will only make it worse.
Thanks again for your input. This is a rather huge issue to get my head around. This is Victoria and most of the trades (insulating and heating) are stuck in a conservative groove. They do somewhat agree with your reasoning. I do to. However, to have those "pros" come in and install as you suggest the bill will be upwards of 6+k. I doubt we will ever see an energy payback for the rest of our years here (we're seniors).
In the 10 years that we've owned this 30 year old rancher, I've never noticed any standing mold, especially on the joist ends. This has been with the vents both opened and closed -- when we purchased the house the vents had been left open for the previous 20 years. Of course, the R13 insulation was only stapled to the bottom of the joists and the rim joists were not insulated at all. This had kept the CS relatively warmer than outside -- but at a co$t of heat loss. All insulation is down on the CS floor right now waiting for a) decision as to what course we will take b) having a knowledgeable contractor agree to our terms of instruction, cost and date.
A single 200-300 board-foot DIY kit for 2lb foam would be suffient material for air-sealing foundation sill and band joist to ~R6 (1" thickness). Then, sealing the interior face of the concrete with a vapor-permeable silane-based sealer will reduce the flow of ground & rain moisture through the foundation slightly, then putting even an inch (R5) of XPS on the concrete, foundation sill, and rim joist will lower the RH of the crawl space by two mechanisms: The XPS is only semi-permeable to water vapor, and insulating the foundation will raise the average temp of the crawl space. A combination of 1" of XPS + a mini-studwall with R11-13 UNFACED rock wool or fiberglass batting (and no interior-side vapor barrier) would be nearly ideal for Victoria's maritime climate. (Great city, BTW- I love the summers there!) I'm not sure if the nat'l builing code has recognized yet that inerior vapor retarders are far more likely to create than prevent problems in coastal BC- you might have an argument with the code inspector on that one, in which case using 3-4" of unfaced EPS instead of 1" XPS (without insulation in the studwall) would put you in the same R-range and is it's own barrier.
With it vapor sealed at the floor, vapor-retarded and air-sealed at the foundation wall, and kept warm enough the the RH stays well above the mold range on the joists, there simply IS no contamination issues by mixing conditioned & crawlspace air.
As for the Advance Energy research summary you linked to , your nowhere NEAR as cold in winter as places like Flagstaff, but you're also nowhere near as DRY, and they didn't insulate the CRAWLSPACE floors, only the crawlspace walls. In all cases the crawlspace stayed much drier with insulated walls rather than insulated floor. In Victoria the subsoil temps are ~10C, and if you insulate the walls of the crawlspace to ~ R10-R20 and the crawlspace floor to ~R8-10 you'd have the best of all worlds. If you insulated the above space floor to R20 between the joists the crawlspace will run colder and more humid. If you go with the latter putting at least half the R value below the joists and air tight (with say, 2-3" of unfaced EPS rigid board, for lowest cost) will keep the joist edges well out of mold/rot danger, and the crawl could be vented to the outdoors. Then again, if the same EPS were laid atop your cement-parge crawlspace floor and insulated the foundation walls you'd be in about the same place, with less labor, and have a warmer-dryer crawlspace. (R8 of EPS will run you about the same money as R5 in XPS, but it'll be twice as thick- you have some headroom to work with.)
In the AE research article they do make reference to insulated floors vis a vis insulated walls :
" Energy Savings
While moisture reduction was consistent, energy
savings varied with climate, insulation and duct
placement.
In Flagstaff, researchers monitored energy use
throughout a single heating season. While the homes
with insulated floors used 20 percent less natural gas
than the controls, those with insulated foundation walls
used 53 percent more.
This seemed counterintuitive; ducts are a notorious source of heat loss. With
all the Flagstaff homes’ ductwork in the crawl space, one would expect better
performance from the warmer, wall-insulated crawl spaces. But according to
Cyrus Dastur, the Advanced Energy building scientist who directed the research,
those homes’ lack of floor insulation let heat radiate from the first floor to the
crawl space, robbing more heat from the house than was saved by keeping the
ductwork warm.
The research makes it evident that in cold climates, it’s better to insulate the floor
above the closed crawl space than to insulate the foundation walls. "
I realize it's Flagstaff, but perhaps adding a regulated exhaust fan (like the Tjernlund unit -- they make a compelling argument for their product) and some tiny amount of make-up air to the CS I can make our plan work. Or, perhaps going back to the other idea of running an HRV air supply and stale air return duct -- with a low wattage in-duct heater -- will accomplish the conditioned air movement required. That is the opinion of the SummerAir folks, who make HRV's.
Another concern is that by making our humungous CS a conditioned area, the CS would have to be heated to near the same temps as upstairs living area. It seems logical that the un- or under-insulated floors will otherwise transfer their heat to the coldest area -- down to the CS and it heatsink floor. Methinks that insulating the subfloor to the max will mitigate this problem.
Have you read David Hill's article on this subject? (he manufactured our Eneready HRV) It is very interesting as it adds a new element of radiant barrier to the mix. I talked with him a while ago, and as a local (Vancouver) he suggested venting the CS with a small exhaust fan. Here's his take on CS modifications:
Radiant Barriers in Crawlspaces Feb. 3, 2010
Although R-2000 attributes little insulating credit to radiant barriers, leading Canadian building scientists 60+ years ago recognized their benefits in housing. Today we thank Dr. Don McAdam for reintroducing this ‘insulation’ to us. Over the last 3 years he has patiently made 2 in-depth technical presentations to TECA members complete with a convincing demonstration and a follow up in TECA News.
While radiant barriers are simple to use and appropriate in specific applications they are complicated to explain. Unfortunately they are misapplied in wall cavities and the poor performance which results has discredited them for use across the board. Radiant barriers shine in retarding heat flow downward*. Attached to the underside of a wood joisted floor system is the sole winter heat retaining application where radiant barriers can be effective.** If the floor is radiant heated floors they are even more beneficial as an ‘insulation’ method.
The total floor heat loss down downward is made up by adding up the 3 separate and independently acting floor losses, conduction, convection and radiation.
Conduction There are 2 downward conduction paths through a wood joisted floor system: conduction through the wood of the joist itself and conduction through the air between the joists. Both losses operate independently. In the case of a 2 x 10 joist system, heat conducts down through both the 9- 1/4" joist itself and also through the 9-1/4" depth of air contained between the joists. Because dry wood has an R value of approx. 1 ¼ per inch thickness, the R value of a 2 x 10 is about R12. Unfortunately, regardless of the insulation material used to fill the joist space, these 2x10’s always conduct some heat. However, in a 16” o/c joist system the path width through the 1 ½” of wood is only 9% of the gross floor area, so this and the fact that seasoned wood is a fair insulator, the conduction loss down through the floor assembly is small compared to either convection and radiant losses. The thermal bridge caused by the 2 x 10 could be reduced by substituting a TJI (with a thin 3/8” web) or by installing rigid board insulation sheathing wall-to-wall under of the joists.
The ‘still air’ between the joists however, is a very good insulator. A layer 9-1/4” thick provides approximately R50. The R value of the assembly drops to approximately R39 after factoring in the lower thermal resistance of the 2 x 10 itself. Dr. McAdam showed TECA members that glass fiber is a less effective insulator than ‘still air’ itself. After air movement has been properly stopped, adding any insulation between the joists displaces the thermally more effective ‘still air which actually decreases the insulating value of the floor assembly.***
Convection When joints and gaps through the perimeter rim joist and holes through the subfloor drilled by the electrician’s and plumber’s are sealed, the air between the joists is heat trapped so it can not move. The upper layer of air in contact with the underside of the subfloor plywood is warmer, making it want to rise thereby maintaining the ‘trap’. This means that convection can not begin.
Radiation In quality draft-free construction, radiation is by far the most significant contributor to main floor heat losses down into a crawlspace. The 70° F floor plywood (80°F +/- if radiant heated) 'sees’ the crawlspace floor. The underneath side of the subfloor plywood is a highly effective heat emitter while the crawlspace floor is a highly efficient heat absorber, thermally a bad combination. It makes no difference whether the crawlspace floor is skim coated over poly or is simply poly. This radiant loss downwards occurs unabated 24/7 all year because the temperature difference between these 2 surfaces is held almost constant all year. A comfortable floor must be maintained @ 70°F minimum while the ground itself holds the crawlspace ‘floor’ to 40°F +/-**** In summary, the radiant loss downward over the period of one year is significant because:
a) the floor area is large,
b) the loss is constant and significant, unlike that of the exterior above grade walls where the losses approach zero during the summer and milder weeks of spring and fall, and lastly
c) a crawlspace, indirectly heated by losses from above will drive increased heat loss to the outdoors.
Radiant Barrier Types Bubble wrap is sometimes used to insulate HWT's. The benefit in this mainly vertical application is the wrap’s built-in compartmentalized air cells. The internal trapped air bubble resists both conduction and convection making the wrap effective. In a crawlspace application, where the barrier is used horizontally however, the bubble wrap’s most significant contribution against downward heat loss are its 2 exterior shiny surfaces, not the trapped air between. Simply, even with its internal built-in R value, the extra cost of the ‘bubble’ product over the simpler flat shiny sheet is not warranted in this floor application.
Summary
1) A double-sided foil radiant barrier tacked to the underside of the floor joists will significantly reduce radiant losses to the crawlspace.
2) Sealing the rim joists and subfloor penetrations will completely eliminate the convective losses through this floor assembly.
3) The net result, ‘still air’ trapped within the 9 ¼” ‘thick’ joist spaces provides conduction resistance that’s superior to traditional 9 ¼” thick R28 batts. That is R39 overall as for compared to R28 for the batted joist system. Note, while the R28 correctly represents the batt’s R value, the ‘assembly’ R is reduced to R25 when one discounts for the effect of the joist’s thermal bridge. Joist thermal bridging was already factored in for the still air’s R39 resistance value.
A foil radiant barrier costs less than batt insulation to purchase and install. Note, a radiant barrier does not have to be sealed to the standards of an air barrier of the plywood subfloor above, for example, so any minor holes left in it to accommodate plumbing and wiring do not seriously degrade its barrier performance.
Radiant Barrier availability The closest source we have found so far is Rona:
L#KLt 1050 SKU: 10010945 Attic Insul Kit Description: 723389 Attic Insulation Kit IK00001-CDA (roll) Size: 500 sq. ft.
Installation
• To Reduce Radiant Heat Loss: After all plumbing and wiring is done, simply staple the radiant barrier to the bottom of the joists. In the case of TJI floor system, there are more effective ways to install the radiant barrier, but they are less practical.
• To Reduce perimeter Radiant and Conductive Heat Loss and Eliminate Convective Loss: Before installing the radiant barrier, install Iso Board in the rim joist cavities, shiny side facing inwards towards the centre of the house. Seal around edges of Iso Board and air leaks around plumbing/electrical penetrations in the subfloor.
Notes:
* Heat moves from warm to cold with equal ease up, down or sideways, only hot air rises. One only has to sit on a cold concrete paver to realize that heat goes down easily.
**In a hot climate, radiant barriers make great heat shields. Shiny foil material may be factory applied to the underside of the OSB roof sheathing, built into a roof tile underlay board and used separately suspended below the roof sheathing or, laid directly on top of the attic insulation. Suspending the barrier, while the least practical, is the most effective as both shiny surfaces contribute to the barrier effect. Radiant barriers effectively block the line-of-sight radiation transfer from the underside of the roof sheathing to the attic floor almost as if the glass fiber attic insulation was not there. Radiant barriers are especially useful when direct sunshine heats the roof surface to high temperature during any season when this added gain would overheat the house.
Note that radiant barriers (for either heating and cooling applications) only work when one or preferably both shiny surfaces have a minimum of ¾” air space in front of them. Their radiation ‘insulation’ properties are reduced to zero in the portion of their area which touches any other construction material.
***Fiberglass batting of floor joist systems is still used today, in part as a legacy from drafty floor systems. However, batting is only a cure to a symptom. The best result which can be accomplished by placing batts here is to slow down the air movement through the joist system. Air leakage through slit openings between the plate and rim joist, joints in the rim joist and through holes in the subfloor causes high convective losses. This could be much more effectively accomplished by air sealing. Dense pack cellulose insulation, while it is seldom used for this purpose is an exception because it is a very effective draft stopper. Evidence of our misunderstanding about joist system air movement contribution to heat loss is easy to see in renovation where pink and yellow figerglass batts removed from between garage/carport ceilings and heated bedroom floors above show large black dust stains from years of filtering the dust from moving air.
**** In locations when the ground is dry and hence has low conductivity and when the crawlspace floor is placed well below grade, 3 feet or more, the crawlspace floor centre may gradually warm up thereby reducing radiant loss from above. However many crawlspaces are shallow, are built in highly conductive wet soil, with some even allowing ground water to pass under enabling them to suck even more heat away. These high loss conditions depress crawlspace floor temperatures increasing the radiation losses from above.
David A. Hill
Note: Dave's process? Easier said than done! In the very beginning of this exercise I did contemplate installing radiant barrier. In the end the product was returned to the supplier. For one thing there it was too difficult to plan out the install as too many integrated utilities (plumbing, electrical wiring) were involved -- under and around joists, etc -- when it's up in place there'll be no map as to where any utilities are hanging. Also, no local insulation installers knew how to put this stuff in correctly. And, I discovered the absolute conductivity of the material frightened the heck out of us : what would happen if any electrical fault touched the massive sheeting of this under-joist install!!
|
|
|
|
|
Dana1
 Senior Member
 Posts:6991
 |
| 28 Oct 2010 06:19 PM |
|
In the Flagstaff floor vs. crawlspace foundation insulation experiement there was only wall insulation in the crawl, with nothing between the crawlspace air and the cold cold dirt (which is about 5C colder in Flagstaff than in Victoria.) With both the walls and floor of the crawl instulated there won't be that huge heat loss going out the bottom. Radiant barrier is all but useless when the temperature differences are less than 20C between the cold surface and hot surface, which is why they have no pay back in applications other than attics in hot climates. Unless the crawlspace got below 0C and stayed there often (not likely, in Victoria), you'd get pretty lousy performance out of it in this application (unless you keep your place 30C indoors all winter. :-) ) It is IN NO WAY equivalent to R28 batts in the joists at your delta-Ts. Your crawlspace floor is closer to 50F (10C) on the coldest day of the year than it is to 40F, if you've closed off the vents. And your sub-floor is closer to 60-65F than 70F (unless you have radiant heated floors.) In Saskatchewan there might be a winter benefit though. But with as little as R5 between the radiant barrier and the sub floor the delta-T between the RB and the crawlspace floor will be so small as to yield nearly zero benefit. But if you stuff R30 batts or something between the joists, the cold edge of the joist will be colder & damper. If you insulate between the joists and ventilate the crawl use outdoor air, and run it on dehumidistat control (which will mostly work in Victoria, but wouldn't in places with higher dew-points. |
|
|
|
|
Daler
 New Member
 Posts:10
 |
| 28 Oct 2010 09:29 PM |
|
Posted By Dana1 on 28 Oct 2010 06:19 PM In the Flagstaff floor vs. crawlspace foundation insulation experiement there was only wall insulation in the crawl, with nothing between the crawlspace air and the cold cold dirt (which is about 5C colder in Flagstaff than in Victoria.) With both the walls and floor of the crawl instulated there won't be that huge heat loss going out the bottom.
Was there something I was not understanding in the AE article? Quote: "While the homes with insulated floors used 20% less natural gas than the controls, those with insulated foundation walls used 53% more." then.. "those homes' lack of floor insulation let heat radiate from the first floor to the crawl space, robbing more heat from the house than was saved by keeping the [ductwork] warm." and.. "The research makes it evident that in cold climates, it's better to insulate the floor above the closed crawl space than to insulate the foundation walls." Well, I think we qualify for cold climate compare to say, Florida
Radiant barrier is all but useless when the temperature differences are less than 20C between the cold surface and hot surface, which is why they have no pay back in applications other than attics in hot climates. Unless the crawlspace got below 0C and stayed there often (not likely, in Victoria), you'd get pretty lousy performance out of it in this application (unless you keep your place 30C indoors all winter. :-) ) It is IN NO WAY equivalent to R28 batts in the joists at your delta-Ts. Your crawlspace floor is closer to 50F (10C) on the coldest day of the year than it is to 40F, if you've closed off the vents. And your sub-floor is closer to 60-65F than 70F (unless you have radiant heated floors.) In Saskatchewan there might be a winter benefit though. But with as little as R5 between the radiant barrier and the sub floor the delta-T between the RB and the crawlspace floor will be so small as to yield nearly zero benefit.
Sure glad I listened to myself on the first time around (and now you are confirming it) -- I felt the hype on that stuff had to be way off here in this climate. Hard to understand why an engineer/designer (Dave) would postulate such a remedy. Anyway, it could have been worse ..but it wasn't installed and the the supplier took it back with no questions 
But if you stuff R30 batts or something between the joists, the cold edge of the joist will be colder & damper. If you insulate between the joists and ventilate the crawl use outdoor air, and run it on dehumidistat control (which will mostly work in Victoria, but wouldn't in places with higher dew-points.
I think we will probably stuff the floor joists, get a Tjernlund ventilator http://www.tjernlund.com/retail/underaire.htm -- it has an integrated humidistat and low-temp shutoff t-stat, and use another opposing vent for a small amount of makeup air (to keep the CS from sucking in living space air). As well, there is an existing 500w baseboard winter-use heater in the center of the CS, as well as a ceiling fan we installed a few years back.
I want to thank you for offering all this information for us to chew on. If the above project doesn't satisfy our needs, then we may look biting the bullet and move on to insulating the walls, etc.
-dale
|
|
|
|
|
Dana1
 Senior Member
 Posts:6991
 |
| 29 Oct 2010 11:23 AM |
|
The issue in the insulated floor article was that the CRAWLSPACE floor wasn't insulated. While insulating the walls of the crawlspace insulated the house against outdoor conditions, it left a big opening to a cold (much colder than yours) heat sink- the earth. They also only insulated the crawlspace to R13, and they didn't measure (or didn't document) the actual air-leakage rates, or the conditioned space temperatures, or the heating duct temp & duct insulation levels, the air leakage rates on the houses, etc. It's a flawed test with incomplete information, on an inadequate foundation insulation job. Outdoor average temps (not average high or average low, but overall mean) in Flagstaff are between -4C & -5C, compared Victoria's +4C to +5C average it's not just a little bit colder, it's a LOT colder, as are their sub-soil temps. Their average winter temps are 5C below Victoria's average low temps, and their subsoil is ~5C below yours, representing a much larger heat loss if neither the conditioned space floor nor the crawlspace floor is insulated. R13 would be about the minimum crawlspace wall insulation most would recommend for you, (the 1" XPS R11-13 batt stackup runs ~R14-R16, with the thermal bridging of the studs factored in) yet R13 that's all that was used in the Flagstaff test. R5 would be about the minimum floor (or crawlspace floor) that I'd recommend in conjunction with R13 crawlspace walls for you, yet they went with R-ZERO in Flagstaff. For Flagstaff R20 walls + R10 floor in the crawl would have made more sense (but could be considered overkill for you.) Winter temp averages in Baton Rouge (the other city tested in your reference) are ~+10C, but with subsoil temps of ~15C so you're roughly halfway between the two. (In central FL winter temp averages are 12-14C- you're definitely a cold climate relative to Florida! ;-) ) With a R30 in the joists, either use un-faced batts , but if they have a facer, be sure the facer is on the top not the bottom. It's easier to install faced batts by stapling the facer to the joists on the crawlspace side, but that would put a vapor-retarder on the "wrong" side of the stackup, potenially trapping moisture that gets in there from conditioned space. Also be sure to put a vapor-permeable AIR BARRIER on crawlspace side of the batting, or it will under-perform it's R-value considerably. Housewraps like Typar or Tyvek would be fine, or thin plywood/OSB- just be sure it has a perm-rating greater than 1 (housewraps are all 10perms+, and go up quickly.) Under no circumstances should you use a poly vapor retarder as your air-barrier at the crawlspace side of the joist insulation. Canadian national building codes may require you to put a vapor barrier between the insulation & subfloor, maybe even poly sheeting, which would be fine if you have vapor-permeable flooring, even though it's not really necessary from a building-science point of view in coastal BC. If you have a vapor-retardent or vapor barrier flooring materials like vinyl, etc. you absolutely SHOULD NOT use any vapor rebarrier below the floor- you can make the (very real) argument to the inspector that adding a vapor barrier below would trap moisture in the structural flooring, with a very high risk of rot. (Use only UN-faced batts in that case as well.) If there are local insulation companies that install cellulose, putting up some 10mm OSB and BLOWING the cavities full will result in a tighter/better-performing result than batts. Whether blown or batt, sealing & insulating the foundation sill & rim-joists with ~2-3cm of closed cell foam keeps wind forces from driving outdoor air into the joist cavities, preserving the rated R of the insulation. (Unsealed rim joists are a very common "thermal bypass" to floor joist insulation, and particularly problematic with low density batts.)
|
|
|
|
|