Thanks for the clarification. By being "fluffed" meaning air was more present in the cellulose, I would of thought it would've acted as a better R. Apparently not! Learning something new every day.
When it's said that 10'' or so gives you R? does that mean that it's at max. peformance when settled at that depth.
Or 10'' reduced to ? when settled gives you R?
It DOES have more R when fluffed 'cuz it's deeper when it's fluffed. But it doesn't STAY fluffed- it settles, and that settling factor has been measured.
The coverage markings on a bag specify the settled-R, but tend to overestimate for real-world installations. In generale it's good to allow for 15% more material than specified by coverage charts on the bag. To meet the manufacturers spec with that coverage requires reading the fine-print: Set up X-manufacturers blower model Y with air settting Z, bla bla bla, and for the most part if you follow the prescription to a T you'll get that settled depth and density (within 10% anyway.)
Real world installation isn't so precise, but if you apply 10-15% more material than on the coverage chart, blowing with as much loft as is "reasonable", the settled depth and R value will meet or beat it, but on day 1 it may exceed it by 15-20%.
The best measure is to wait 10-15 years, measure the depth and assume something like R3.5-R3.6 per inch. But for us with less patience, buying the extra material and shooting 15-20% high on installation day is close enough for all practical purposes.
eg. If you want R35 at settled depth that's ~ 10", so set your cardboard depth markers to 11.5-12" and make sure it's that deep on installation day, independent of blower settings. On day 1 it'll be ~R40, but in a decade or two it'll be more like R35, and won't drop much from there. In your 7-8" overblow situation, shoot for 8" and you'll still have better than 7" settled-depth.
There are occasional reports of "fluffing" blown insulation in the industry, but I haven't heard of any real egregious operators since the early '90s. This was more common with blown fiberglass, that sometimes takes forever to settle, and has real performance issues if installed at too low a density. With over-fluffed cellulose the performance is OK, but the settled depth well below what the manufacturer specified. Find somebody who's been in the biz for awhile and has a good rep, and you'll be fine. Or if a DIY, just give yourself more margin, and count the bags & square feet for a rough estimate of your installed density with the beater rental-blower.