A metal roof IS a vapor barrier. Putting a second vapor barrier on the interior of the roof assembly would keep open cell foam from ever drying should there be a leak. To meet code you need an ignition barrier between the foam and the interior space though. (Half-inch gypsum, or most 3/8" OSB or plywood would qualify.) Since you don't want to build a ceiling, you probably don't want to build a cathetral-ceiling either? There are spray-on ignition barriers that would work, but for the money you'd be better off going with 2" of closed cell foam at the roof deck with 3" wet-spray cellulose or superfine wet-spray fiberglass (JM Spider) blown-in-bag on the interior for the ignition barrier, which would boost the R up to ~ R23-25, compared to R21-22 for 6" of o.c.SPF. The wet-sprayed goods have water-activated adhesives- once they're up they stay in place, and won't need gypsum or wood for support on the interior. (IIRC it takes 3" of either to be legal.)
|