Posted By JeffInCO on 16 Jan 2011 04:23 PM
Thanks for the replies...
I'm just east of the Rockies in Colorado, where we struggle to keep the interior humidity at 30% in the winter... Without running a humidifier, the interior humidity would drop to 20% or lower.
I am in the process of insulating the garage, and eventually heating it with radiant heat from the slab (already insulated to R-10 underneath and around the perimeter). I plan to keep it at 50-60 in the winter; I suppose the HRV exhaust could easily be colder than that, which would make my idea not so good.
I was trying to think of a good way to provide some air flow in the garage as I think it is unusually tight with 1" of foam in the exterior walls and doors that seem to close very tight as well -- no visible light around the perimeter of the garage doors. The living space portion of the house is off-the-scale tight, hence the need for an HRV, at least according to the free energy audit from our electric company. (The auditor recorded 2 air changes per hour WITH the blower door in place, with a "C8" fan configuration and 814 CFM through the fan. The conditioned portion of the house is about 4000 square feet with an average ceiling height of about 8 feet).
Jeff
The dew point of 30% RH 70F air at 5k' of elevation is 37F- anything in the garage that's at 37F or lower would be at risk of condensation, and even if the garage is 50F the RH in the garage would still approach mold-growth levels with a constant supply of HRV-cooled conditioned space air that started out at 35%RH/68F.
Installing the little Panasonic
FV-04VE1 single-room ERV for the garage-only could provide at least some ventilation to a tight garage without introducing moisture, or cross-mixing garage air contaminants into conditioned space air etc. It maxes out at 40cfm, but can be set lower (10-20cfm) if desired. ( A 25'x25'x10' garage would still get ~2.5ach @ 40cfm.)