We are hoping that the existing plywood decking is in good shape after we tear off the shingles . Could we put a layer of OSB then Deck Armour on top of the strapping and then the metal shingles ? Would condensation be an issue then ? There is a product called Enkamat by Colbond that is a nylon mesh ventilating underlayment that can be used under metal roofing that could possibly be used to provide some ventilation to prevent condensation. We do not know of anyone who has used it. Also, we will not be able to obtain R-50. We will only be able to add two inches of foam board especially if we allow room for an airspace.
The amount of air space you'd need depends a bit on the roof pitch- at high angles it doesn't take much. ANY amount of air space (even through mesh) is a huge improvement over laying metal-on-felt or metal-on-OSB. It doesn't prevent condensation, but it does allow the roof deck to dry toward the exterior rather than accumulate moisture over time. Using mesh solutions helps keep the gap from becoming a home for critters too- it's not a bad way to go.
Radiant barrier in air gaps less than an inch or two don't add much. But using a high solar-reflectance high-infra-red emittance finish on the exteior cladding does a LOT during the cooling season. For comparing apples to apples/pears, use the database of product testing data available at
http://www.coolroofs.org/.
At 2" you get ~R12 out of iso during the cooling season, maybe R10.5-11 during the depths of January, but that would be more than sufficient to allow you to do a high-density full-cavity fill on your 2x4 rafters rather than just the batts without any risk of rotting the roof deck from below with wintertime condensation from air leaks & vapor diffusion from the interior.
Low and mid-density batts leak air and convect like crazy lowering their effective R during the winter, and are translucent enough to infrared that the hottest part of the batt ends up being about an inch-in from the outer surface, making them effectively R7-R8 under a 120F roof deck in July. Filling the same cavity with cellulose or high-density new-school blown fiberglass (1.8lbs density Optima or Spider) eliminates the derating due to convection loss, giving you a stable & honest R12-R14 year round. With R10+ on the exterior you don't need (and shouldn't use) interior vapor retarders, but if they're there (kraft facers on batts etc) it still probably isn't worth ripping down the ceiling to remove them. It's often possible to dense-pack over batts without removing them, but if they're easy to pull, it's easier to install the blown goods without them. With R10+ on the roof deck the temperature difference across the batt is lower though, so it's R value derating is also lower- it might be comfortable enough with a just a cool-roof w/ R10-ish exterior foam solution.
Also note, R10-R12 over the roof deck improves the whole-assembly R more than you might think, since t's placing a thermal break over the rafters which would otherwise be conducting both directions. R12 foam + R13 batt/blown may only add up to R25 center-cavity, but it's the energy-equivalent of ~R30 between rafters or joists due to the much-reduced thermal bridging at the rafters.