Posted By harv11733 on 24 Nov 2011 08:35 AM
Thank you for your reply. A heat load calculation was done with a determination that an output of 90,000 btu would be sufficient for heating. I'm not sure if this includes the domestic hot water for a separate 50 gallon water heater. Since the old boiler is not functioning it is not possible to determine the return water temperature.
The Alpine 150 has a 150 btu "input". The next one down is 105 btu "input". I don't want to oversize but am concerned the 105 is insufficient.
Also is a "condensing" boiler best for my situation of cast iron base board?
What's your location? (so we can look up your design condion outdoor temp and annual heating degree days.) That 90KBTU heat load number seems high by at least a factor of 2, maybe as high as three, based on your fuel use.
eg: A 65 year old cast-iron boiler is probably only running 75% efficiency, at best, which means you're getting (0.75 x 138,000=)~100KBTU out of each gallon. Let's say you live in Worcester MA, (my current home town. :-) ) with about a 6800 heating degree day (base 65F) and a 99th percentile design temp of 0F. In 6800HDD you used 1300 gallons which is ~0.91 gallons/HDD, or (100,000 x 0.19=) 19000BTU/HDD. There are 24 hours in a day, so that's 19000/24= ~800BTUs per degree- hour.
Your design temp is 0F, your HDD base temp is 65F, so the difference is 65F degrees. At 800BTU/degree-hour and 65F heating degrees at design temp, you need at most something with an output of (65F x 800BTU/F-hr=) 52,000BTU/hour.
Given that in an old boiler standing by all summer at elevated temp to deliver the domestic hot water probably burns 200gallons/year on hot water heating, the odds are your 0F heat load is under 45KBTU/hour.
If your old boiler is 4-5x oversized for the load, poorly insulated and has never had the heat exchangers refurbished your actual efficiency is going to be under 60%, and your design condition heat load correspondingly lower. But tell us where you are, and we can use real weather data & design temps.
It's important to get the SMALLEST unit that actually meets your design condition heat load, even with a modulating-condensing boiler, even more so if the system is divided into separate zones, since the smallest zone will have an average heat load well below the maximum output of the boiler, and probably below the minimum modulated output even on design day. A boiler that short-cycles on zone calls will have lower operating efficiency and will wear out sooner.
It would take a very large, underinsulated and drafty-breezy house need
the full output of the Alpine 105 in my neighborhood, and it's
min-modulation might be more than half your design condition load, which would mean it can't be tweaked to modulate perfectly with load- it'll cycle on/off more often than it otherwise might need to if it were "right sized" for the load. The Alpine-80 modulates down to 16K-in but the -05 only goes down to 20K, and the -150's min-mod is 30K (which is more than 80% of my design day heat load, let alone my average.) If you upsize to the 150 and your actual design condition load is 35-45K, it's bound to always cycle on zone calls rather than continuously modulate except on the coldest days of the season.
Cast iron baseboard is GREAT for mod-cons, compared to fin-tube since it has many times more thermal mass, which makes it less prone to short-cycling the boiler, and a more predicatable output at lower water temps- you can get far more condensing efficiency out of it than you could with fin-tube, and it's far less likely to run into short-cycling problems even at low operating temps, unless it's been micro-zoned, with a separate thermostat in every room.