Posted By lzerarc on 22 Jan 2012 11:33 AM
gusto
Mitsubishi makes a hyper heat model, that can provide 100% efficiency at 5 degrees and 70% (or something like that) below 0. It is rated down to -14 or so. They come in 9k btu and 12k btu models. They run around $1500-2000 online plus install. My plan for our SI house will be one of the 12k units on the main floor and another in the basement. 2' baseboard heaters will be placed about 1 in each bedroom for backup heat as needed. Hopefully they do not need to run often at all.
It is true as temps drop the COP of the HP lower as well. However they are typically still above 1, or what the electric baseboard heaters would be.
Either option comes much below the install cost as infloor heat.
Make that "100% of rated output at 5 degrees" and "70% of rated output at -13F". At +5F they're running ~150-200% efficiency (COP 1.5-2.0), depending on compressor speed. They come in more than the 3/4 ton & 1-ton models too. At mid-speed most heating mini-splits will run a COP better than 2.5 @ +17F.
In most of US climate zones 5 & 6 a mini-split will have an average COP of 2.5 if sized exactly to the design condition heat load (which isn't always possible in zone 6, but can be in zone 5 in a superinsulated house. Oversizing it by ~1.5x it will add ~0.5 or more to the average COP since it will spend most of it's time running at lower & more efficient compressor speed. In US climate zone 4 it's pretty easy to heat seasonal average COP > 3.0.
Electric baseboard have a COP of 1, which means it'll run use 2.5-3x the electricity of a mini-split. Your electricity would have to be practically free for this not to make economic sense in a net-present value analysis, even with low heat loads & superinsulated houses.
You have to place the interior heads where they won't blow on humans, and this is even more so if you oversize, since the bigger you go, the more air it moves. At some point oversizing becomes less comforatable, even if it's more efficient.