| 12 Jun 2012 11:55 AM |
|
I am planning on putting an air handler and ductwork in my attic to handle heating and cooling to my 2nd floor. As part of the same project, I am adding insulation throughout the house. My attic runs the full length of the house and at the peak is about 7' high. In order to bring it into the envelope, I was thinking of doing the following: -Flash and fill the floors to airseal (going back and forth about open cell vs. closed cell for this application) and use lots of cellulose to bring up the R value -Sprayfoam the ducts with closed cell foam (I've read that open cell won't hold up to the vibration) -Build a box around the air handler with EPS or XPS foam and make sure one side could be opened for access to filter, etc.
Some questions: 1-Is this a good idea and if so, what are the code issues I need to be aware of? 2-Do I foam underneath the ductwork and airhandler or just around and on top of since the point is to allow it to be part of the envelope? 3-What moisture and access issues should I pay special attention to? I've seen air handlers in attics that have drip pans but if I insulate properly, I don't know if this is still in issue. Also, if I'm putting all the ductwork under foam, it does make it a little harder to get to in order to repair or make any manual airflow adjustments, I presume.
|
|
|
|
|
|
|
Dana1
 Senior Member
 Posts:6991
 |
| 12 Jun 2012 12:26 PM |
|
The cc foam on the ducts needs an ignition barrier to meet code. IIRC 3" + of cellulose would qualify. In a vented attic with air-permeable cellulose, the underside of the duct is still going to be colder than the outdoor dew point in humid climates, and will experience condensation if it doesn't have air-impermeable insulation on the underside as well. (Whether the cellulose would adequately buffer that depends on the climate and the cooling load, but fully insulating the ducts is more assured.) |
|
|
|
|
geodude
 New Member
 Posts:58
 |
| 12 Jun 2012 02:31 PM |
|
I have done this exact thing before. In retrospect, I would have pushed for a foamed in unvented attic. It just performs better. On another note that drip pan is a secondary pan in case the internal condensate pan fails. Most codes will require this for an attic unit. |
|
|
|
|
Dana1
 Senior Member
 Posts:6991
 |
| 12 Jun 2012 04:00 PM |
|
If there's any way to bring the ducts & air handler fully inside the conditioned space (or go ductless) it makes sealing the attic/conditioned space boundary easier and more reliable, and presents far fewer headaches down the road. By the time it's said and done it's sometimes cheaper & better to do as geo-dude suggests, make the roof deck the pressure and thermal boundary of the top of the house rather than the attic floor. |
|
|
|
|