Posted By morlock on 26 Jul 2012 09:08 AM
I've read a few books from the 70s that talk about cool rooms and earth tubes, but haven't seen much action on these techniques. I assume they don't really deliver then?
I typically discourage the long term storage of alcohol. It's a clear indication you're not drinking it fast enough. Now storing your friends wine... I think you're on to something there.
Earth tubes prove problematic from a fungues & mold point of view in places with the summer dew points as high as yours. It can be done and done right, but it is more trouble than it's worth unless you have a VERY stringent specification to meet.
It does not take a huge fan/duct to reduce or eliminate air temperature stratification over 30' of height, but it's not going to provide effective cooling- the heat-exchange with the subsoil is too inefficient to handle house-sized cooling loads.
You may be limited by the historical commission on what you can do, but reducing the direct solar gain from windows & roofs is the first line of cooling load reduction. CRRC rated "cool roof" materials come in a lot of colors other than "white", and is moderately more effective than radiant-barriers on the interior. Awning overhangs shading south facing windows kills a lot of window gain- the killer to treat would be east or west facing windows. Exterior shades work best but if you're allowed to install heat rejecting low-gain windows that would still be worth it.
I'm curious how you're insulating on the interior of the brick, and a bit concerned about how you're handling bulk-water issues at the windows & doors. Older uninsulated buildings rarely had any window & door flashing, and relied upon rapid drying to the interior to handle any moisture loads. Also, insulating between the brick and the interior leaves the brick at a lower temp, and some consideration has to be made for wintertime moisture/condensation loading issues where the structural joist timbers meet the brick.