Variable speed Well pump
Last Post 13 Sep 2012 05:50 PM by jonr. 4 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
whirnotUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:186

--
09 Aug 2012 10:42 PM
Someone was telling me that there are new Variable speed (VFD) well pumps out now that save a lot of energy.
Anyone familiar with them? From what I have found there are some that are variable speed and eliminate a large pressure tank but really no talk of energy efficiency. the speed difference eliminates the pressure changes. It would seem to me that they would always be working against almost max pressure and thus be less efficient, but I might be looking at it wrong.
jonrUser is Offline
Senior Member
Senior Member
Send Private Message
Posts:5341

--
10 Aug 2012 09:55 AM
I say min pressure, but even so, not a lot of energy . Say your conventional tank varies from 30 psi to 50 psi. A variable speed pump could be held right at 30 psi.
whirnotUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:186

--
10 Aug 2012 12:29 PM
IF it did hold to 30 then there would be some savings as it would never be pushing against 50 psi. Typically VFD's save a lot, but I just have not been able to find info on these.
SkyHeatingUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:203
Avatar

--
13 Sep 2012 05:40 PM
I cannot fully speak on the savings because I don't know much about well pumps but I do work with ground source heat pump flow centers and a typical flow center for a 3 ton unit uses about 400 watts while a variable speed pump can flow more water at a higher head pressure and do it for about 120 watts. I can't tell you much more than that.
Visit my Youtube channel for product reviews and customer testimonials http://www.youtube.com/user/skyheating1
http://www.welserver.com/WEL0626/
jonrUser is Offline
Senior Member
Senior Member
Send Private Message
Posts:5341

--
13 Sep 2012 05:50 PM
There is no free lunch in pumps. If you have a predictable load and a properly sized/rated pump, you will actually lose a little efficiency in the electronics of the VFD. A VFD is beneficial where the load is variable.