Posted By toddm on 29 Aug 2012 07:54 PM
So, in summary, your comparison of R5 full underslab insulation coverage in your addition vs zero sub slab in the original house tells us nothing about the relative comfort merits of full slab vs perimeter (and slab edge which icf gives you in the addition). The perimeter counts; the middle doesn't. In normal soil anyway. IIRC, you have water table issues as well.
You don't dispute that full slab coverage saves very little money. You don't dispute Basecalc's estimate that a Minneapolis basement in January loses heat from the middle of the slab at the miniscule rate of 0.67btu/sq ft/hr. Yet, somehow, sloooow changes in midslab make a major difference in comfort. How? And where is the proof?
Your summary misconstrues and assumes a lot.
BaseCalc is (and always was) by definition crude estimate and doesn't account for the radically different thermal characteristics of different soil types & moisture levels, etc., and focuses entirely on heating costs, ignoring latent load AC or mold risk factors. BaseCalc is better than a WAG, but it's numbers should always be viewed with large 1-sigma error bars. (IIRC it tends to shoot to the high side of measured heat loss.)
Did somebody state that mid-slab insulation made
ANY difference in comfort? (I sure didn't.)
My understanding is that PassiveHouse modeling is much better on precision end, but the cost of the soil testing & groundwater surveys required to narrow down whether you actually NEED that extra R15 or whatever to meet the Passivehouse energy use requirements would be higher than the cost of R15 of EPS. (I've never read of a PassiveHouse design where all factors were actually measured.) In some ways the BSC recommendations may suffer from a similar fudge-factor- at 10cent/R/square-foot it's cheaper to install the recommended values than to analyze whether it could get by at half those values for any particular site.
You recall correctly that the average water table isn't very far below the slab at my house. If anything the in-situ observations between the insulated and uninsulated slabs regarding slab temp & mold risk would tip the balance in favor of full-slab insulation as relatively cheap insurance.
The notion that slab-edge insulation several feet below grade on walls with R18 insulation that extends to a few inches above the slab (and below the 100 year design frost depth) would somehow raise the center-slab temperature above the summertime dew point is absurd on the face of it. But it's true that my older slab has no slab-edge insulation.
The situation Marc Rosenbaum ran into in his Martha's Vineyard house where the house was built with an insulated slab but without foundation-wall insulation, and a batt-insulated basement ceiling, it would be a structural hazard in US climate zone 7, (or even the colder parts of zone 6) and much of Canada. By insulating the slab and the basement ceiling yet not the walls the direction of heat loss at the slab is reversed in winter, since the basement falls below the ground temperature. Frost heaves grow in the direction of heat loss, and with a sub-freezing basement at the 100 year frost-depth design extremes it could buckle the foundation wall or the slab. With insulated foundation walls on a heated house, even if the heat loss is low, the direction of the heat flow is always from the basement to the ground, and will never be going the other direction in frozen soil. (In US zone 5 that risk is pretty tiny even for slab-on grade, and easily avoided with code-minimum slab edge insulation.)