Posted By philipmhowe on 25 Oct 2012 11:33 PM
I’m thoroughly intrigued as to why you would want to do
this. I can see wanting to insulate (isolate) the chimney from the main part of
the house, but I would think it rarely necessary to insulate a chimney. I would
think the only advantages of an insulated chimney would be to a) perhaps reduce
heat-up time for a chimney that is not regularly used or, b) improve draft on a
chimney that has very marginal draft.
Also, wherever possible, I like my chimneys exposed, so that
I can keep an eye on their response to environmental conditions (acid etching
of mortar, fractures due to whatever structural/thermal stresses are occurring, poor
masonry, etc.)
In re-reading, I note “Insulating the below the roof line is
intended primarily to lower the heat load rather than improving the draft,
since there's already an insulated stainless liner inside the old
terra-cotta for dealing with drafting issues.” That takes care of the draft
issue.
It seems to me that the major improvement would result from properly
sealing the fireplace to prevent air leakage (primarily) and possibly conductive heat
transfer (a very poor third). How this should be done would depend upon
intended frequency of use. Anyway, you have my interest.
PMH
Lemme 'splain ya:
The fireplace and brick is already pretty tight, without huge passive air leaks. (Compliments, to whomever installed that flue liner & stove!) Air leakage isn't the issue, conducted heat is:
When the wood stove isn't burning and they're using the boiler system to heat the place, at the outside design temp of 5F with a 70F room temp the 100 square feet of ~R2 of masonry would be conduction (100 x (70-5)/2 = ) 3250 BTU/hr out of the house, which turns out to be roughly 10% of the whole-house heat load of this particular house at that design condition.
When the wood stove is cookin' along and brick in the firebox is running more than 120F (usually would be at LEAST that when trying to heat the whole house on a cold day) the heat loss would be about doubled, reducing the effective efficiency of the wood burner as a space heater. Insulating the chimney with R15 continuous insulation will reduce those losses to about 12-15% of their current levels.
This chimney was re-pointed about 15-20 years ago (as reported by homeowner- the exact date uncertain) with a hard mortar, and it's a hard brick, all in GREAT shape. The house has ~2' overhangs, and the chimney penetrates the overhang- the lower portion of the chimney has much less rain-washing than the portion above the roof line. Buttoning the chimney up behind siding and insulation means it would see even less moisture transfer and lower thermal stresses than it has seen in it's nearly 100 year lifespan to date. If the inspector insists on a lime-mortar parge for further protection it wouldn't be a big deal, but it doesn't really seem called for, given how solid it is despite it's age. It's supported by a poured concrete foundation, and shows no signs of efflorescence anywhere.
Moving it inside the thermal & pressure boundary of the house wouldn't be any different than chimneys running in chases up the centers of other houses. Since insulating it will make it warmer & drier on average, I see no reason why it wouldn't last another 100 years or more, just like any brick chimney built into a chase indoors.