Posted By Lee Dodge on 31 Dec 2012 03:27 PM
Posted By Dana1 on 31 Dec 2012 02:29 PM
...snip...
A 30K max with a sub-15K min would be pretty reasonable for these smaller to-mid sized houses with design condition heat loads in the 20-25K range. I'm sure the house with a 14K load @ design condition would be just fine with that (hypothetical) 15K/30K furnace. And it would be both more comfortable & efficient than a 60K single stage bang-bang or 60K/30K two-stage.
My natural-gas furnace is a mod-con 60 kBtu/hr max / 21 kBtu/hr min, and I would not mind trying something a little smaller, as a thought experiment anyway. However, I have not seen the efficiency curves versus load, so there is no reason to expect an efficiency improvement with such a change.
I had the temperature set down yesterday since I was out in the snow, and it reached 60 degF last night around 4:30 AM. I noticed that the furnace came on at 4:30 AM this morning to try to reach 67 degF by the 6:15 AM set time. It starts out cranking at full output for about 1/2 of the temperature recovery and then throttles back after that. I suspect that the efficiency is better at the lower firing rates, due to both lower air pressure drops through the ducts and longer residence times in the heat exchanger, but that is only a guess. Going to a higher average firing rate by downsizing the furnace could be counterproductive in trying to increase efficiency. I really need to see (or generate) an efficiency versus output power curve to be able to answer that question.
It's fair to say that at 2x oversizing there isn't an efficiency hit, but at 4x oversizing it might be- it depends on many factors. (Work done at Lawrence Berkeley Nat'l Labs back in the mid 1980s indicates there may even be an INCREASE in efficiency at 2x oversizing for bang/bang single stage condensing furnaces. I can look that up for you if you like.)
Most multi-stage or modulating condensing furnaces run at higher efficiency at their min-fire, and the benefits of setback strategies are potentially (but rarely) negative, since they almost always kick into the lower efficiency high-fire on the recovery ramps. In your case 4x oversizing may be good enough to simply keep it from hitting high-fire most of the time, since the setback temp is probably only rarely achieved due to the high mass of the house (?). But with a set & forget strategy and a furnace with 15K min-fire output it would also NEVER kick into high-fire mode with a 14K design condition heat load. You're in a position that you can probably instrument your setup to track it in both setback and set & forget modes for several weeks at a time and measure it's performance against HDD weather data to see if the setbacks are actually buying you anything with your modulating furnace's and your house's mass/heat load characteristics. Low mass high loss houses actually hit the setback temperature values far more often than high-mass high-R houses, but a high mass house that loses any significant temp in the overnight would almost always induce a high-fire response on the recovery ramp. I'd be interested to see how yours measures out, even if it's just a single data-point, and an atypical house.
One of the guys in my office lives in a town-house heated with a 2-stage 60K/30K condensing gas furnace (like almost every other unit in the complex where the original ~100k single-stagers have bitten the dust), and he has hacked the internal controls to keep it from ever running at 60KBTU/hr. Yes, the recovery from setback is now longer, but not enough to matter. He's never measured or calculated the heat load, but it's almost certainly under 20K, and may be under 15K after the insulation and air sealing he's done over the past 3-5 years. (The biggest and leakiest unit in the complex probably still comes in under 30K, despite crappy leaky 1980s construction.) I'm sure he'd be happy to see a 30K-max 2-stage on the market by the time the current unit is toast.