Most of the footings are now well inside the thermal boundary of the additions, and unless you've insulated the slab and footings everywhere else and have a very high performance standard you're trying to meet there's nothing really worth insulating on what are now load-bearing partition walls. It may be worth insulating the first 5-8' of the wall that intersects the new exterior wall, but it may also be possible to cut the old CMU wall at that intersection and insert insulation there. (That would be my first choice, if it doesn't XPS is blown with HFC134a, which has ~1500x the greenhouse gas potential of CO2. Using 2.5" of EPS (blown with pentane at only ~7x CO2) is a lot friendlier to the environment. EPS is at least as moisture-tolerant as XPS, with a long history of being used for flotation in marine environments. Cellulose is often problematic in basements, and a disaster if the basement has water/drainage issues. Second choice would be rock-wool, followed by dense-packed new-school fiberglass (Spider, Optima), which won't wick or hang onto water to anywhere near the extent cellulose does. Third would be open cell foam. Whatever you fill the cavities with, put an inch of rigid EPS or XPS foam between the bottom plate of the studwall and the slab as capillary & thermal break. Compression strength doesn't matter- the studwall only holding up the gypsum & insulation, not the house. |