Posted By dkinion on 16 Feb 2013 10:57 AM
Thanks for the detailed reply. Seeing as the roof was done with the house I'm not interested in tearing it out for the above the roof deck approach you recommended. How would it even be possible to hit R38 only insulating from the inside. 5.5 in of open cell only gets me to R19?
It's basically NOT possible to hit R38 in 5.5". If you have space to add thickness below the rafters you can get there, but it has to be semi-permeable to water vapor to avoid creating a moisture trap.
OK (like most states) has yet to adopt IRC 2012, and your statewide building codes are
currently based on the IRC 2009.
Under IRC 2009 the legal code-minimum is
currently only R30 for all but the panhandle region. With 2.5" of unfaced rigid EPS insulation under the rafters & spray foam behind the ceiling gypsum you'd be there, and it would still have sufficient vapor permeability to avoid trapping moisture, yet sufficiently vapor retardent to not have wintertime accumulation issues. If you can, use two layers (1" + 1.5") with the seams staggered, which mitigates against heat leaks opening up should the EPS shrink a tiny amount over the next couple of decades (which it usually does.)
Alternatively you could use 2" of XPS (pink, blue, green, doesn't matter, as long as it has no foil or plastic facers) it would get you there too, but it would be a the absolute limit from a moisture release point of view. If you have the clearance for the extra half inch, unfaced EPS would be better, with about 4x the drying capacity. XPS is often available with ship-lap edges, which would gets around the double layering/shrinkage issue. While there are also tongue & groove variants, ship-lap edges are better for this purpose.
With an R10 rigid foam between the ceiling gypsum and the R19 open cell cavity-fill in 2x6 rafters you would have nearly the same performance at ~R30 as you would get from low density R38s in a 2x12 rafters, which isn't bad. Assuming a 15% framing fraction, with the 2x6 + R10 foam it's ~R25.5 for "whole assembly-R" with all thermal bridging factored in, compared to ~R28 for the 2x12 /R38 situation. By contrast, the code-min R30 batt in 2x10 rafters runs about ~R23 after thermal bridging, so the foam-under is ~10% higher performance than a typical R30 installation.
Do NOT use Rmax under the rafters, since it has aluminum facers, which would create a severe moisture trap.