Posted By cladano on 19 Feb 2013 12:25 PM
I'm building a new home and the builder/framer/lumber company screwed things up. The plans for the house called for 2x6 exterior walls with R19 bat insulation. They installed 2x4 walls.
I would still like to get an R19 value out of that 2x4 wall. One insulation guy I just talked to was trying to pitch me a BIB L77 Insulation that has a "true" value of R15, that he said would be just as good or probably better than R19 bat insulation. I've also read that closed cell insulation would have a good R value. Not sure what options are out there or what would be best.
Any suggestions or thoughts would be greatly appreciated!
Thanks,

At a 20% framing fraction an R19 batt wall comes in at ~R13.5 for the "whole-wall" R, with all of the framing factored in.
At the same framing faction an R13 batt wall comes in at about R9.5.
If you pounded in L77 or Spider at R4/inch (R15) only raises the whole-wall performance to R9.75.
How much are you willing to pay for R0.25? Slipping in 1/4" XPS siding underlayment would give you R1 or so, but that still wouldn't hit the performance of the 2x6 wall.
Even if you put 3" of R7/inch closed cell foam in the 2x4 cavity it still comes in at ~R10.5. (A full3.5" fill isn't practical with closed cell foam, since trimming it flush with the stud edges is nearly impossible.) That's about the same as the 1/4" XPS underlayment under a full-cavity-fill of mid-density fiberglass or cellulose.
If you add one inch of rigid EPS insulating sheathing to the exterior of the 2x4 wall with R13 (damp spray cellulose, open cell foam, or perfectly and I mean PERFECT R13-R15 fiberglass or rock wool batts) it will be equivalent to R19/R21 in a 2x6 wall.
If you add 2" of exterior foam and used 2 layers of foil-faced polyiso, seams staggered and taped with FSK tape (both layers), at the same wall thickness as a 2x6 wall you're now at ~R21-R22 whole-wall, which is a significant improvement over your original design.
In general sprayed or blown insulation has far fewer voids and compressions than batts. R19 batts are truly bottom-of-the barrel goods- they weigh the same per square foot as R13 batts- they're just "fluffed". Low density R22s aren't significantly better, but high density "cathedral ceiling" batts are the real deal (and the price shows it.) With any compression or void the amount of air convection & infiltration through the material is HUGE compared to higher density goods. Rock wool batts are comparable in density and performance (and price) to the high-density fiberglass batts, and are in some ways preferable (fire resistance, and fewer issues with binders outgassing, no issue with suspended micro-particles floating in the air, etc.) But damp sprayed cellulose is often cheaper than high-density batts (and definitely cheaper than L77 BIB), and far greener in most respects.
So, if I were in your position, I'd hold out for an inch or more of foam and damp-sprayed cellulose. Rather than long-nailing through the foam causing 10,000 thermal bridges to ruin the performance, use 1x4 furring through-screwed to the studs 24" o.c. to give you something to hang the siding on, leaving a "rainscreen" air gap, which allows both the sheathing and the siding to dry better/quickly. It's always better to use 2 layers of foam and stagger the seams, but you can also be OK with 1-2" XPS (pink, blue, green, whatever) with ship-lap edges (not the t & g), which keeps heat leaks from opening up as the foam shrinks slightly over the next couple of decades. Tape the seams with housewrap tape, and foam-seal the edges with can-foam or FrothPak.
Caulking the studs to the sheathing in each stud bay and every seam at the stud plates/subfloor/band-joist/foundation sill interface with acoustic sealant caulk can make the wall assembly more air-tight than merely insulating the stud bays with spray foam, and is about the cheapest performance upgrade to the thermal performance of a wall you can buy. (Foam seal every electrical penetration of the studs too.)
With enough foam-R on the exterior you can skip interior vapor retarders, which makes the assembly more resilient to wetting events.
The minimum amount of foam necessary varies by climate. If you don't know your climate zone, find yourself on
this map. For reference, an inch of EPS is ~R4, an inch of XPS is ~R5, and an inch of iso is ~R6.