Posted By chaz on 18 Jul 2013 08:05 PM
There is no flashing to speak of unfortunately but I did go to the trouble of caulking the exterior well last summer when I painted it. Hopefully this did not seal the siding and where it butts against the house too tightly since what you suggest requires the ability for the siding to breath somewhat. Otherwise I'm not sure where the 1/4" gap behind the siding would move moisture to. If I was to use foam board, would it make sense to just use a thin piece covered with a fiberglass or some other air permeable insulation from a cost perspective? The wall cavities are actually 5" deep in most areas due to shimming the walls plumb so they could accept something like I described.
The rafters are 2x6 but since they are exposed at this point I could easily make them deeper to allow for air space and more insulation. But as is stands now, there would be no where for that air to go as there is no ventilation for the roof. Though I suppose I could just add a ridge vent easily enough.
The basement is air sealed and insulated only at the rim joists and where the top of the block foundation meets the sill plate. However the basement is conditioned to an extent by a a few vents.
The crawl space is like the room above. It is only siding nailed to the framing.
Is there a product that could seal the foam board in the cavities or do I just rely on a spray foam?
Thank you so much for your reply.
If you have 5" of stud depth to work owith, put 1" of rigid EPS with a ~1/2" nominal gap to the siding, to allow a 3.5" nominal cavity depth, and use unfaced R13 fiberglass (or R15 rock wool) for the rest. Use some cut-down foam as spacer blocks/strips for the offset to the siding, then use can-foam to seal the EPS to the studs. Expanding foam (eg Dow Great Stuff) or 2-part polyurethane (eg FrothPak) are the only suitable materials for reliaby sealing rigid foam between the studs, and it'll pretty much glue it in place permanently. (It's chemically similar to Gorrilla Glue.)
If you have a source for reclaimed roofing foam (check craigslist) and can find some 4" EPS or iso, or some combination of thicknesses that adds up to 4-4.5" that would be quicker & better (and often cheaper) than a foam + batts solution.
The vent space has as much to do with being a reliable capillary break as it is a true vent, but venting it to the exterior (even if only at one end) will give it much better resilience, particularly on the roof deck. You can get round retrofit soffit vents
as small as 1" , but bigger would be better. If you're adding 1.5" of depth to the rafters and venting the rafter bays, do it with 2 x 2s perpendicular to the rafters, and put either high-density R15 "cathedral ceiling" fiberglass or rock-wool R15s in the rafter bays, and use split unfaced R19s compressed into the 1.5" micro-cavites. Better yet, put R15s in the rafter bays and add 1.5" polyiso rigid board on the underside. Either of those solutions provides significant thermal break over the R1.2/inch rafter timber, delivering measurably better thermal performance. If taking the rigid-iso road, tape the seams with 2" FSK tape (aluminum duct-tape) for a fairly reliable air seal, and stagger the seams of the gypsum with those of the iso. But putting 2" of iso above the roof deck and installing rock wool R23s in the 2x6 bays would be higher performance still. (The big box store chains carry Roxul these days.) With foam above the roof deck you'd need to add a nailer deck for the shingles. Holding the foam in place with 2x4 furring through-screwed to the rafters 24" o.c. with pancake head timber screws and putting a 1/2" or 5/8" OSB nailer would be the preferred method, since you could then vent the channels between the furring with Cor-A-Vent or similar. But if that stackup is too tall to work, an OSB nailer flat to the foam through screwed 24" o.c. works too (but may have to be replace if the roofing ever leaks.)
The higher the R-value an more air-tight you make the roof assembly the less likely it is you'd end up with ice damming problems. In zone 5 ideally you'd be able to take it up to R50 or better, but if you deal with the thermal bridging of the rafters, even R35 is pretty good. With R23 batts tight to the underside and 2" of iso above the roof deck you're looking at R35 nominal at center cavity, and would have sufficient exterior R from a dew-point control point of view, but 3" of exterior foam would be better, and it would take 4" to actually meet IRC 2012 compliance. If you do a combination of thickening up the rafters 1.5" AND exterior foam, 3" of exterior iso (R18-19) would be necessary for dew-point control.
In zone 5 it's long-term cost effective to insulate the basement with 1" of EPS on the exterior and an interior side 2x4 studwall with R13-R15 batts (unfaced batts only), foam-sealing the EPS to your band-joist foam. Slip an inch of EPS under the bottom plate of the studwall too, as a thermal & capillary break from ground, which has moisture wicking through the slab.
Treat the walls of the crawlspace in the same manner as the room above, but put a 10-mil poly vapor retarder on the ground. Is there a poured or CMU foundation for the crawlspace, or is the porch supported by piers, cantilevered with the house framing or...???