Posted By DENALI on 28 Oct 2013 05:30 PM
My climate zone is 4A but the 4A/5A border is about 15 miles to my north. My zip is 67575 for reference. What about putting a 1.5 inch average closed cell spray foam in the cavity then using the intello plus or membrane and blowing in loose fill like articat to finish off the cavity? Then drywall over it? Thanks
If you put 1.5" of closed cell in the cavity there is no point to the Intello Plus. The 1.5" of foam is more vapor-retardent than the Intello when dry, and has the same or greater R-value as the 2" of AttiCat. If you're going that route, a 1" foam is actually better, since it it's enough R to keep the average mid-winter temp of foam/fiber interface above the ~40F dew point of the interior air, and gives the roof deck better drying capacity. But you don't really even need that. Your
mean outdoor temp in January is about 32F, but the average temp over the 3 coldest months is about 38F.
In your climate just open cell foam or dense packed cellulose would be just fine, and would cost about as much as the 1.5" of closed cell. Open cell would be more air-tight, cellulose would be more protective due to it's moisture buffering capacity. You could also dense pack the cellulose to make it nearly as air-tight as open cell, but dense packing would likely cost more than half pound or 0.7lb (Demilec) open cell foam. If you're a DIY batt kind of guy, cotton batts have a similar R and moisture buffering as cellulose. If you like playing with insulation blowers, you can use landscaping fabric stretched tightly and stapled ~4-6" o.c. on the rafters as blowing mesh, then see what you can get out of the single-stage rental blower for the box store- you can probably hit 3lbs density or so with cellulose, which is pretty good. After blowing you can roll it flat to the studs with a rolling pin or section of 3" PVC or something before putting up the gypsum.
Cellulose has a summertime performance edge over fiberglass in attics & cathedral ceilings due to it's higher opacity to infra-red. With a hot roof deck the "as used" R-value of the first inch to two inches of fiberglass won't quite meet spec due to the penetration of radiated heat through the translucent fiber at high delta-Ts. (The ASTM C 518 test used for labeling is 75F center temp with a 30F delta-T, which isn't half as severe as a 140F roof deck with a 75F air-conditioned interior.)
When you re-shingle it's worth putting up ~R20-ish nailbase iso above the roof deck (R15 min, to meet IRC 2012 code) bringing the center cavity R to over R30, with a good thermal break over the rafters. There's is a rationale for more if you're heating with propane, but not a lot more.