Posted By ibilisi on 23 Feb 2014 10:34 PM
Hello all,
I've been doing research on the best way to insulate/retrofit my rim joists, a 1931 stucco home. My floor joists sit on top of block foundation walls. The spaces between the joists have been filled with sloped/pitched concrete.
Now, I understand 2" of 3lb foam is common, as well as polyiso or xps foamed in place. However, I've also been looking at the research from building science regarding embedded beams, in which they state that "However, static thermal simulations indicate
that there might be significant risk of wintertime condensation within the cavities at typical interior humidity conditions, based on the beam pocket surface temperatures relative to indoor dewpoints."
I have not seen my specific case discussed anywhere, as roughly half of the beam is "embedded" in the sloped concrete. In addition, it may be possible to remove all of the sloped portions, but then I am not sure of how they are attached to the rim and would 2" 3lb foam provide similar structural effect (if that is the purpose of the concrete)
http://www.buildingscience.com/documents/confpapers/cp-1201-masonry-wall-insulation-interior-embedded-beam-simulations
Use of 3lb foam is actually pretty rare in this application, but 2lb foam is common. The most common application for 3lb foam is sprayed-on insulating roofing.
Climate matters in this decision, as does the amount of ventilation space behind the stucco and the rim joist/sheathing, and what type of weather-resistant layering (asphalted paper, rosin paper, or whatever) is between the stucco & sheathing/rim-joist. Where is this house located, and what is the stack up?