General Forum - Residential
Conditioned Crawl air return
Last Post 30 Jul 2014 09:56 PM by
GAD
. 4 Replies.
Oldest First
Most Recent First
Prev
Next
Author
Messages
GAD
29 Jul 2014 04:49 PM
I recently purchased a house with ICF walls and a conditioned crawl. When I was checking out the crawl space it has a air supply from the HVAC unit, BUT it also has a air RETURN.
Is having an air return in a conditioned crawl space okay,safe and or normal???? Thanks for your help
joe.ami
30 Jul 2014 09:07 AM
In many jurisdictions, a crawl must be conditioned space(requiring both a supply and return) or all the duct within should be insulated so it is not uncommon practice. The only places returns are generally dis-allowed in residences are kitchens, baths and areas from which combustion air is gathered (i.e. mechanical room). Common pratice is also to avoid laundry rooms.
One old practice used the crawl space as a return air plenum. Still permitted in many municipalities as long as vapor barrier is in place and walls are insulated, return air grilles would simply be placed over a hole cut in the floor and the furnace would draw return air from the crawl.
30 Jul 2014 09:32 AM
Pressuring or depressurizing any space will cause leakage (to the outdoors). So you want a supply and a return in almost any closed area - properly adjusted to produce a neutral pressure.
BadgerBoilerMN
30 Jul 2014 09:49 AM
Yet another way to warm your floors!
GAD
Thanks for your replies! Makes me feel way better!