In a zone 4 climate vapor barriers (and even closed cell foam) can be more of a risk than just dense-packing an offset double-studwall. Adding 1.5" of closed cell foam inserts a ~0.75 perm class-II vapor retarder into the mix, and if it's on the interior side of the exterior sheathing it creates a condensing surface, increasing the wintertime moisture uptake of the cellulose, limiting it's ability to dry toward the exterior, and limiting the ability of the sheathing to dry toward the interior. While it'll probably still work, it's a net cut in resilience.
It's useful to have a vented rainscreen space (as jonr suggests) between the siding and exterior sheathing, and have at least 1' of roof overhang per story (both at the eaves & rakes) to limit bulk-water penetration.
If you install any vapor retarders at all, an interior side "smart" vapor retarder like Intello Plus or Certainteed MemBrain would offer a modest amount of resilience, but it's not really necessary in your climate.
Code does not require vapor retarders of any type for zone 4A, but if you're putting vapor retardent foam on the exterior side of the assembly it's better if it's R-value is more than 16% of the total R (
as in the prescriptive stackup for marine zone 4C) .