Posted By arkie6 on 06 Nov 2014 05:47 PM
Where are you located? Given this is for a basement, If your deep earth temperature is 45 deg F or less, 1.5" of 2# density EPS foam will out perform 1.5" of polyiso due to polyiso's characteristic drop off in R value as its temperature drops below ~60 degrees F. And the EPS foam should cost less assuming you are purchasing new material. And the EPS is essentially unaffected by ground moisture and has a stable R value over its lifetime (polyiso and XPS drop off in R value as they age).
That's a gross overstatement of the performance roll-off of polyiso. Given that it would be on the INTERIOR side it would be warmer and at a temperature where it may even outperform it's labeled R-value.
Only when the MIDDLE of the polyiso or EPS is at 45F would EPS outperform it. (That scale is "mean temperture" of the foam not the exterior or interior side temperature.) If it was all polyiso and the room was 65F, a mean temp of 45F would require a ground temp of 25F (permafrost!) for EPS to be at par with polyiso.
With ground temp of 45F and a room temp of 65F, the polyiso would in fact beat it's rated R, since at a 55F mid-foam temp it is near it's absolute peak performance. (Which occurs at at
mid-foam temp of ~60F.)
But even the cold side of the polyiso is warmer than 45F. With an inch or two of XPS between the polyiso & ground the polyiso will perform at it's labeled R (or better) in any location in the lower 48 states.
Where polyiso derating is an issue is when it's on the cold side of the assembly in a very cold climate, with insulation between the polyiso & interior.
At any labeled R value EPS and polyiso are usually comparable, but XPS commands a 20-30% premimum.