Is vapour retarder really necessary if you have adequate ari barrier and exterior insulation?
Last Post 20 Dec 2014 05:40 PM by Dana1. 33 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Page 1 of 212 > >>
Author Messages
edithUser is Offline
New Member
New Member
Send Private Message
Posts:16

--
10 Dec 2014 01:36 PM
We have 4" of EPS on our exterior wall and a meticulously taped sheathing and attention to detail as an air barrier. We will also be blowing dense pack cellulose into 8" wall cavities. We were hoping to avoid a vapour retarder but are we being foolish?
We are in zone 7 (I think) - Ottawa, Ontario.
JohnyHUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:114

--
10 Dec 2014 02:32 PM
Zone 4?
JohnyHUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:114

--
10 Dec 2014 02:36 PM
I think your biggest issue is the building inspector!
edithUser is Offline
New Member
New Member
Send Private Message
Posts:16

--
10 Dec 2014 03:25 PM
I've always thought it was zone 7 but I certainly may be wrong.
We are in Quebec actually, just north of Ottawa. No inspectors of the building elements. Just inspections for tax purposes...
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
10 Dec 2014 03:28 PM
Read this.

Yes, Ottawa with ~4500 HDD (Celcius)  is pretty similar to the cold edge of US zone 6. With 4" of EPS you're looking at R16-R17 on the exterior, and with 8" of dense pack (or is that a 2x8 studwall and thus only 7.25"?), you're looking at R28-R29 in the wall cavites, so the exterior R is about 22% of the total R.

IRC 2012 specs for zone 6 are insulated sheathing of  R7.5 or greater for a 2x4 wall (with R15 batts that would make the exterior foam 33% of the total R), or greater than R11.25 for a 2x6 wall (with R23 in the 2x6 wall that would also mean 33% of the total R in exterior foam.)

So, for Ottawa you'd need about 50% more exterior foam to skip interior vapor retarders completely, but with a smart vapor retarder such as MemBrain it should be fine.
edithUser is Offline
New Member
New Member
Send Private Message
Posts:16

--
10 Dec 2014 04:33 PM
OK thanks Dana. We bought Insulweb to install our cellulose but I imagine Membraine or the SIGA Majpell would work too. Anyone interested in buying our Insulweb?!
edithUser is Offline
New Member
New Member
Send Private Message
Posts:16

--
10 Dec 2014 11:26 PM
Just realized that we have already closed up the walls of our walkout basement. So the knee walls (the basement is stepped) have roxul in 8" stud bays and 4" of EPS on the exterior. Are we at serious risk of having condensation on our sheating?
tjetsonUser is Offline
New Member
New Member
Send Private Message
Posts:52

--
11 Dec 2014 03:55 AM
edith, i would think so, I had frost issues just recently in winnipeg albeit with only 1.5" of foam on the outside. I ended up drying the place out and putting up membrain
edithUser is Offline
New Member
New Member
Send Private Message
Posts:16

--
11 Dec 2014 10:13 AM
So what about latex paint? It is a calss III vapour retarder..
edithUser is Offline
New Member
New Member
Send Private Message
Posts:16

--
11 Dec 2014 10:15 AM
Dana, our wall would be 7.25" dense pack cellulose. And the basement is 7.25" roxul
jonrUser is Offline
Senior Member
Senior Member
Send Private Message
Posts:5341

--
11 Dec 2014 10:46 AM
I agree, use MemBrain and detail it as carefully as your exterior air barrier.
maxvdhUser is Offline
New Member
New Member
Send Private Message
Posts:15

--
11 Dec 2014 11:01 AM
Edith, you can do the same calculation Dana did to check: 4" of EPS (~R16) + 7.25" of dense pack (~R26) = R42 total. R16/R42 = 38%, so you have an acceptably large proportion of exterior insulation to omit the vapor retarder. With Roxul, the R-value for 7.25" is 28-30, so your ratio could decrease to about 35%, which is still acceptable per IRC 2012. The reason tjetson had trouble with frost, assuming he has the same stud wall thickness and insulation as you, is that he doesn't have enough exterior insulation to keep the temperature of the condensing surface between the foam and the studwall above the dewpoint temperature.

I believe that a coat of vapor-retardant latex paint on the interior is a good plan with that type of wall stackup. Feel free to correct me if I've misunderstood your wall stackup.
edithUser is Offline
New Member
New Member
Send Private Message
Posts:16

--
11 Dec 2014 11:14 AM
Great news. Thanks.
Our original plan was to used 5" Roxul board on the exterior but found it to be too expensive. We felt confident with that stackup to omit the vapour retarder.
I think we will probably use Membrain or Majpell on the rest of the house...
maxvdhUser is Offline
New Member
New Member
Send Private Message
Posts:15

--
11 Dec 2014 11:22 AM
Actually Edith, before you jump for joy I'd like Dana to comment on this again. I am second guessing myself because he's really the expert but I don't see how he came up with his estimate that you're at only 22% exterior R. His calculation should have come up with nearly the same number as mine (a little lower since he was basing his off of a full 8" of dense pack). Dana?
edithUser is Offline
New Member
New Member
Send Private Message
Posts:16

--
11 Dec 2014 01:15 PM
I get the same calculation as you. I am comfortable with latex paint in the basement, or even a vapor retarder paint. But I will use a vapor retarder other than latex paint on the rest of the house. The other details, such as moisture management outside, attention to detail re. air barrier also give me confidence. And I will be keeping a close eye on the RH indoors.
maxvdhUser is Offline
New Member
New Member
Send Private Message
Posts:15

--
11 Dec 2014 01:27 PM
Very good. Maybe Dana was thinking it was a double stud wall, which would get you R56 in the wall with a 22% exterior R.
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
11 Dec 2014 06:24 PM
maxvdh has it absolutely right- mine was an arithmetic error- MEA CULPA!!

I apologize for that- (need more coffee, and no more doing it in my head at the end of the day...)

With 7.25" of cellulose you're looking at at worst R26-R27 for cellulose layer, and if it's Type-II (1.5lb per cubic foot nominal density) EPS you'd be looking at about ~R18 performance or better during the weather that matters. So assuming R45 total you're in the 40% range, which is just fine.

Thanks for catching that maxvdh!
maxvdhUser is Offline
New Member
New Member
Send Private Message
Posts:15

--
11 Dec 2014 09:35 PM
No thanks needed Dana, I owe you a huge debt for all the knowledge I've managed to accumulate from reading your posts. If you're anywhere near Andover I feel like I owe you and your family a dinner out for all the help with my future home design.

And Edith, I'm glad we've confirmed that your walls are in good shape!
FBBPUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1215

--
11 Dec 2014 11:53 PM
The latex paint only works if you use air tight drywall techniques include locking in around electrical boxes.
edithUser is Offline
New Member
New Member
Send Private Message
Posts:16

--
12 Dec 2014 08:26 AM
Thanks to you both!
FBBP, this brings up a point that I have often wondered about. We have dedicated our sheathing as the air barrier. I also like to think of it as a pressure boundary. So vapor will not be drawn through our walls because there shouldn't be holes drawing air into our walls (through our sheathing). So in a sense the vapor retarder is not needed at all, but in my case I am using it as a precautionary measure. I have no doubt that we have an imperfect air barrier but we've done the best we can.