Joel1226
New Member
Posts:3
31 Dec 2014 03:50 PM
Need to determine best way to insulate single slope parallel chord roof. Chords are 24" in depth. Standing seam metal roof with sturdy vent baffles between the 24"OC trusses. Ceiling will be either T&G pine or ship-lap pine. Plan is to blow in fiberglass. Question, what is the best way to create the vapor barrier on the interior side? We have looked at 6 mil poly, MemBrain, or 1/2" foil faced foam.
Attachment: parrallel_chord.jpg
Bob I
Veteran Member
Posts:1435
04 Jan 2015 03:55 PM
Install spacers against the roof sheathing, then install plywood or foam board to create a 1-1/2" air space. Once that is done, blow in your dense pack fiberglass, cover with Mem-Brain and strapping, then the T&G. DO NOT penetrate the membrane with nails. If you are using nails of a length that will go through the membrane, then use thicker strapping. Poking holes in the membrane will create air leaks which can be a disaster.
Bob Irving<br>RH Irving Homebuilders<br>Certified Passive House Consultant
kenora
Basic Member
Posts:145
04 Jan 2015 05:21 PM
I hope I can pile on...
I have a similar roof already assembled (20 years ago) so there is 6 mil poly behind the drywall already..since I can't add insulation into the cavity can I add 4 inches (or more) of either EPS or XPS to the interior...bonding it onto the drywall (or nailing/screwing if needed), then T&G boards as above..
I'm also in zone 7 (feels like zone 700 this morning... -32c)
jonr
Senior Member
Posts:5341
04 Jan 2015 05:32 PM
then install plywood or foam board to create a 1-1/2" air space.
I'm curious - what purpose does this non-vented air gap serve?
Joel1226
New Member
Posts:3
24 Mar 2015 06:05 PM
Won't you get nail holes thru the membrain from the strapping? I already have 2" spacing against the roof sheathing (Plastic baffles)and it is vented at soffits on low and high side of single slope roof.
Bob I
Veteran Member
Posts:1435
24 Mar 2015 07:26 PM
I assumed it was vented; it should be. Depending on the membrane, some have tapes that you use where you'll be nailing, but most will seal well enough from the pressure of the strapping.
Kenora: Use EPS which has some capacity to breathe.
Bob Irving<br>RH Irving Homebuilders<br>Certified Passive House Consultant
Joel1226
New Member
Posts:3
24 Mar 2015 08:01 PM
Bob:
Forgive my basic questions. I have gotten so many different opinions! My contractor said just staple up 6 mil poly, blow in the insulation and put your boards on.
So, the membrain is stapled to the bottom of the chords, then the strapping goes over the staples? What exactly is the strapping material?
I thought I could just install the membrain, tape the staples, and then nail the T&G.
You are not authorized to post a reply.
Green Building Forums
--General Forum - Residential
--General Forum - Commercial
--Green/Energy-Efficient Design and Planning
--Green/Energy-Efficient Building and Construction
Green Building Technologies
--Insulating Concrete Forms (ICFs)
--Structural Insulated Panels (SIPs)
--Radiant Heating
--Geothermal Heat Pumps
--Solar and Wind Power
--Windows/Doors and Interior/Exterior Finish
--Appliances, Lighting and Kitchen/Bath Fixtures
Feedback/Support
--Rules, Instructions and Announcements
--Suggestions/Feedback
--Testing Area
Forums
>
Green Building Forums
>
General Forum - Residential
Active Forums 4.1
Membership:
Latest:
croccohvacusa
New Today:
0
New Yesterday:
0
Overall:
35027
People Online:
Visitors:
233
Members:
0
Total:
233