I sincerely doubt that CA Title 24 requires you to use fossil fired HVAC. If that's true I'd like to know the chapter on verses for that. Pros in the know seem to think heat pumps are allowed:
http://www.title24express.com/what-...e-24-hvac/ I'm not sure why the mini-split is being shot down by the tech- the reasons matter. It could be that even the smallest mini-split is too oversized for your actual loads? The model selected had to low an HSPF or SEER?
Or is it the room to room distribution problem.
If it's the latter, a 1-ton mini-duct cassette mini-split like the Fujitsu 12RLFD can have the output split 3 ways, and has an HSPF of 11.5, SEER of 20, and would likely still cut it capacity-wise it on the low-temp end for almost all CA locations west of the Sierra:
http://www.fujitsugeneral.com/PDF_06/Submittals/12RLFCD%20Submittal.pdf
There's a 3/4 ton version and a 1.25 ton version too, if that makes it or breaks it. The efficiency numbers on the 3/4 tonner are higher, at HSPF 12.2/SEER 21.5:
http://www.fujitsugeneral.com/PDF_0...mittal.pdf
A 3-head multisplit would be absolutely
hideously oversized for your likely loads. I suspect your heating loads are under 10,000 BTU/hr unless you have a huge amount of window area (which would also drive the cooling loads sky high), and if you don't have much west facing window area the peak cooling loads are probably no more than 12,000 BTU/hr. But fer yuks, what's the ZIP code, so we can figure out your
99% & 1% outside design temps and take a WAG at it?
Would a ~$1000 heat pump water heater like the GeoSpring make the grade?
It's a lot more money than a propane HW heater, (but it's cheaper to
install) and a heluva lot cheaper than rooftop copper donations to the
meth-addicted party fund