Looks pretty clean!
How much clearance is there between the top of the head and the ceiling? (Looks kinda tight.) According to the drawing on page 10 (PDF pagination) of
the manual you're allowed to be no closer than 50mm to the ceiling, but more is usually better.
How far above grade is the bottom of the compressor unit? Is it protected by roof overhangs?
As for the BTU output, those numbers are credible. The extended temperature capacity tables found on page 16 of that inexplicably stops at -5F, but shows it can deliver 18,600 BTU/hr @ -5F into a 70F room.
The extended temperature capacity tables for the 15RLS
2H found on page16 of the
RL2H tech manual shows that it can deliver 15,000 BTU/hr @-15F into a 70F room, 15,400 BTU/hr into a 65F room. But it only delivers 16,700 BTU/hr @ -5F, compared to the 18,600BTU/hr @ -5F for the 15RLS3.
Given the generally higher capacity of the RLS3s relative to the RLS2s, I'd believe 16,500 BTU/hr @ -15F for the RLS3, even though it doesn't appear in the extended temp table.
Mind you, in some conditions the defrost cycles at super low outdoor temps will cut into that a bit, but it would be a rare stretch of weather indeed for it to persist long enough to notice.