Posted By paulhutton on 22 Apr 2016 07:31 PM
thanks so much for the detailed response, it answered my questions but rose 1 more. I have replaced flat roofing in the past and found that when i had deck rot i found the batt insulation touching the underside of the sheathing. So naturally i assume that if there is no air space it will condense. So the question becomes what allowable amount of air space is mininmally required to avoid condense. in an unvented roof rafter.
In the current situation number 1 there is 6 inches easy above so i look good for another 1.5 poly iso on the deck I was not going to add vapour barrier here since it is already under the drywall.but in situation 2 with about 16 inches total air space from deck to bottom of second set of rafters it appears it wont matter at all if 100% of the insulation is above the roof deck.
Thanks again for setting me straight i was under the impression that by creating 2 insulated areas with air gap in between moisture would trap and condense and cause problems for my clients down the road.
With the fiber touching the roof deck there isn't sufficient air flow to purge moisture that gets in. With the air gap any condensation/adsorb from interior moisture drives begins on the cold ends of the insulation fibers, but unless the gap is vented to the exterior it will still get into the cold roof deck. The amount of space required depends on the pitch of the roof, the amount of free air ventilation to/from the outdoors, and amount of air leakage at the ceiling plane. If it's sealed up drum tight from the outdoors, it's at risk with or without the air gap.
But if you put sufficient insulation on the exterior of the roof deck to keep it's temperature at or above the dew point of the conditioned space air, moisture will not condense on (or more accurately, adsorb into) the roof deck, and no air gap with access to outdoor air is needed.