Posted By arkie6 on 22 Jun 2016 07:58 AM
Current plumbing code requires at least one 3" vent through the roof. You can combine the individual vents in the attic. Maintain 1/4" slope/foot on the horizontal vent pipes in the attic down to the vented components. Use sanitary Tees turned upside down for connection to the main vent stack (upside down relative to installing them for waste flow).
This page shows a sanitary tee installed incorrectly for a vent (it needs to be flipped over to allow free flow of gasses into and out of the vent stack): https://www.nachi.org/bbsystem/viewtopic.php?t=7724
The present pipe coming up & through the roof from my shower is 1.5" diameter. The other, with the toilet, laundry & sink is only 2.5". If I attach a sanitary tee with 2.5" x 3" x 3" & attached the 2.5"to the 2.5" vent pipe, and going up through the roof with 3" and over from the 1.5" with a 3" line coming over from the shower, would that vent everything ok?
Also, about the 1/4" slope/foot on the horizontal vent pipe... does it slope back to the 2.5" vent, so I would cut the 1.5" pipe a little shorter?