Posted By minotto disegno on 18 Jan 2017 02:27 PM
I'm planning a moderate size home in SoCal in a semi-desert climate with adequate thermal mass.
The home will have a tight envelope and my understanding is that some sort of ventilation system with separate duct work is required.
I was planning on an air-source heat pump to meet heating and cooling needs, but this will only be used in the summer and winter months mostly.
Does anyone know if there is a manufacturer that makes an energy efficient, dual HVAC/ ventilation system that would satisfy both of my needs and eliminate the need for 2 duct systems?
<!--[if gte mso 9]>
If you're looking to be misled, you have been so far. I’ll
try and set you on the right path since I’m a Cali peep too
Ventilation…
Anyone that thinks or suggest you build an air tight home w/o knowing what you
are doing does not know what they are doing or suggesting. Most get it wrong, think air will de-tox
toxic building materials, chemically make them inert and stable by some miracle....some
even think that they have to have symptoms, if they don't everything is fine. Plenty
of unseen toxins that produce none until it’s too late, like cancer.
Uninsured DIYs designers take on personal injury liability.
You'll get all the ill-advice you want on green sites, the problem is they
won't be there to hold your hand in court. Check out the lucrative booming IAQ
corrective action business on the internet.
You need a COMPLETE understanding of ASHRAE 62.2 just for starters, preferable
prior builds in accordance with to advice. 2016 is out and the fact nobody has
mentioned it tells you they are not pros. In it you’ll find what I stated above
as disclaimers.
In it you'll also find required OAQ test per NAAQS to determine if a
ventilation sys is possible and, all kinds of local outdoor intake air &
separation restrictions to meet, pressure & flow rates, or it could be VERY
damaging to occupant’s health.
Also, that in Z1-2, sounds like you are in 2b(hot/dry), you don’t need mechanical
ventilation you can use window method unless you mechanically cool, OR, you
have a heated building (natural or mechanical) for less the 876 hours/yr. If you
do need one you have to calculate the flow rates and there is a natural air
credit depending on blower door test or one of 5 ways to calculate it.
Thermal mass is handled different than highly insulated in
dry climates. You’ll focus on HRVs vs ERVs.
Once you understand the whole house and local exhaust (bath/kitchen,
etc) requirements then you shop.
There are also variable/continuous & real time vent combi
systems. …. Then you have to decide if you want your health in your hands, or
auto-scheduled in accordance with a controversial std.
These are good certified products: http://hvi.org/proddirectory/
Then the system has to be further tested beyond the blower
door to verify it to the std, to verify contaminated air is not being
infiltrated, back flows, etc. If a ductless like Lunos, Zehner, Vents-US is
used no more than 10% tested by manufacture, so you have to know what to look
for.
HVAC
You can design a ducted air-source HP tied to ventilation systems, may make
better sense if there are existing ducts and one does not have easy access to
run minisplit refrigerant lines.
or, you go ductless splits best for new construction.
Zoned systems are best. You have to determine peak heating
and cooling loads first using ACCA manual J8 or ASHRAE RLF.
A little history,
The physics involved in the transfer of heat and energy
between buildings, occupants, and the environment is quite complex. The most
current and best math models of this problem require significant input data and
thousands of calculations in an iterative process. The calculations are so
involved that researchers have been forced for years to create various
simplified procedures that are doable by hand or within reasonable calculation
time on a personal computer. The cost of these simplifications from the
theoretical best math models is accuracy, especially residential.
Problem with MJ8 most popular is the way it handles
walls/roofs/glass, thermal mass, ventilation, & other assumptions. Now
making it less accurate we have thermochromic glass with SHGC ranges. It also
uses weather conditions not local TMY weather towers, hard set points, allows
oversizing compared to load which is often the case.
I use EnergyPlus and WUFI computer simulations for hygric
loads. It blends all building component loads, and I can compare designs for optimization.
I’ve seen as much as 40% difference between simplified MJ8 & complex E+
simulations. Right now I have one MJ8 is estimating 33,000 BTU/hr, E+ 12,000, so
I weigh that w/MJ8s successful track record vs more accurate whole building E+
computer sim. MJ8 is typlically 15-20% higher. Manual S places limits on oversizing or under can lead to issues especially dehumidifying/cooling.
So my MS design for a 2348 SF two story loft is 4 zoned,
one 12K, (3) 7K (two of which are daisy chained to other rooms), BTU HP units….there
is no need for excessive temp differences between rooms. Open vaulted 18 foot
peaks costing ~ 8K BTU/hr.
Minisplits are sized for peak cooling loads or heat removed
both latent (low in dry bulb climates with thermal mass like you) and sensible…..In
my and your cases it exceeds heating, if not it can be sized for cold climates
retention.
Cerv is an demand control (DCV) ERV with limited misleading IAQ monitoring, not whole house HVAC, again as noted above and in ASHRAE 62.2 requirements for. Rare you only have < 5k btu/hr loads. Today, we have better IAQ monitors...another complex science only WUFI_BIO can pre-determine with proven high levels of accuracy.
Not to scare you off but be warned when it comes to your health you may want to seek pro-advice and pay as required for it.
Good luck!