ERV CFM confusion
Last Post 28 Oct 2020 11:25 AM by newbostonconst. 19 Replies.
joelwheeler802User is Offline
05 May 2020 08:51 PM
Hi, I'm new here, hoping someone can help me with figuring out the CFM I need for an ERV unit that I'd like to install.
I have an old warehouse building that was gutted of insulation and we just sprayfoamed the ceiling (6") and walls (3") of what will be our living area. It has a full basement under the space. The area is 30'x50' with 15.5' high ceilings. The only room which will be completely walled off from the rest of the space is the bathroom. It will be just a one bedroom structure for myself and wife and 2 dogs. The bedroom will just have half walls so still pretty open to the rest of the house.
I'm getting confused with the CFM calculations. I thought because the ceiling was higher than typical construction that I'd need to calculate cfm by volume, since most of the calculations I found did it by square feet. The first calculation that I found on an HVAC site was:
RequiredCFM = (RoomVolume x AirChangesPerHour) / 60min
Using a chart there that showed that average house air changes per hour looked to be around 7, which also matched what I was seeing on wikipedia, I plugged in the numbers and ended up at 2712cfm. (  [(50x30x15.5)x7]/60 ). Needless to say, I couldn't find any units even close to this so I knew something was definitely off there.
I looked on this forum and found this calculation here http://www.greenbuildingtalk.com/Forums/tabid/53/aff/14/aft/85703/afv/topic/Default.aspx:
"ASHRAE 62.2 calls out 7.5 cfm per occupant plus 0.03cfm per square foot...ASHRAE counts "occupant' as the number of bedrooms + 1"
So, now we're talking (7.5x2) + (1500sqft x 0.03) = 60cfm. That looks substantially more reasonable than 2712.
Then I started reading more about "ASHRAE 62.2", looking on https://hvacdesignpros.com/2012/05/ashrae-62-2-construction-calculate-required-amount-ventilation/ (granted, I see the date there in the URL of 2012 so perhaps this is dated?), where it states that for "whole building requirements" I should multiply the square footage by 1% (.01) instead of the .03 suggested in the quote above. So that puts me at 30cfm. OK, so, 30 or 60, not a lot of difference there in either direction.
But also on that page it states "local building requirements", by room, with the following:
"Kitchens = Minimum 100 cfm of intermittent ventilation or 5 air-changes-per-hour of continuous ventilation"
Since I've got just one big room should I be using this 100cfm number? How do I translate that to continuous ventilation cfm?
And, back to my original concern- none of these calculations use room volume, only sqft. Does that matter?
I don't want to oversize the unit as I've read that you can get excess heat loss. And I don't want to undersize it because I want healthy air.
I'm probably way overthinking this like I tend to do but I appreciate any insight anyone can provide. Thanks so much in advance.
sailawayrbUser is Offline
06 May 2020 10:50 PM
Yes, volume matters in the sense that your goal is to change the entire volume of stale air in a building with fresh outdoor air some number of times per hour to maintain a healthy indoor environment for people. The volume of a building can be calculated as the square footage times the average ceiling height. Ventilation units are either in Cubic Feet per Minute (CFM) or Air Changes per Hour (ACH). Buildings are sealed to different degrees which allows natural air infiltration to occur to some extent. 1.0 ACH or more is typical of older, leaky building construction. 0.5 ACH is typical of new construction. 0.35 ACH is typically the minimum allowed for health reasons and is often accomplished in airtight, energy efficient building construction by using a basic air ventilation system, Heat Recovery Ventilation (HRV) system, or Energy Recovery Ventilation (ERV) system.
ASHRAE 62.2 calls out 7.5 CFM per occupant plus 0.03 CFM per square foot of conditioned space. ASHRAE counts "occupant” as the number of bedrooms + 1. ASHRAE 62.2 assumes an average ceiling height of 8 feet, so you can relate this to volume if desired.
Building Science suggests that this ASHRAE number is too high, and recommends 7.5 CFM per occupant + 0.01 CFM per square foot of conditioned space.
If allowed, we recommend using the Building Science number and proportionately increase it if your average ceiling height significantly exceeds 8 feet (e.g., if your average ceiling height is 10 feet, increase it by 25%). Local building codes often specify what is allowed and some inspectors don't allow deviations.
loghomebuilderUser is Offline
16 Jul 2020 07:19 PM
Posted By sailawayrb on 06 May 2020 10:50 PM
Thanks for your advice. Do these ervs have variable speeds? And what would control the speed? Some of them claim to have a 'max' airflow of some figure, which implies they could be dialed back. Also, why would one pick an HR over an ERV? I'm in Western NY, our house has no AC, and it's a log cabin that maintains fairly higher humidity through the winter. I've gotten mixed reviews from people. What better for me? Is one more efficient than another?
16 Jul 2020 10:18 PM
HRVs and ERVs are similar devices in that both supply fresh air to the home and exhaust stale air outdoors while recovering energy from the exhaust air in the process. The primary difference between the two is that a HRV only transfers heat while a ERV transfers both heat and moisture which translates to energy. Well-sealed homes will greatly benefit from using these devices.
The better option between a HRV or ERV depends on your climate and specific needs. If your house is too humid in winter (above 60% RH) then an HRV is the better choice, as it would help get rid of excess humidity while an ERV would tend to keep it at a high level. If the opposite is true and your house is too dry in winter, then an ERV would be a better choice as it helps retain humidity, eliminating the need (and cost) for you to generate it through other means.
Ventilation speeds are usually MIN, MAX and INTERMITTENT (e.g., 20 minutes ON and then 40 minutes OFF, repeating each hour) and controlled manually via switch interfaces or the device itself. Normal daily operation is typically MIN and occassionaly INTERMITTENT. MAX is typically activated from switches in bathrooms for obvious reasons. Likewise, stale air inlet registers are typically located in bathrooms and fresh air outlet registers are located in living space rooms.
17 Jul 2020 12:41 AM
Last winter my indoor humidity was 50%. Would you go ERV??
I'm retrofitting my unit into the home, so I won't have switches in the bathroom controlling the unit, or anything like that. If I install it myself. Should I just let it run on intermitten or something?
17 Jul 2020 01:29 AM
30 to 50% RH is generally considered the ideal range. So I think you could go with the HRV and run it on MIN or INTERMEDIATE based on where it takes your RH. Presumably, given that you don't have one now, your air quality isn't too bad. So I would size it properly or even a little less and don't over size it. And by size, that could be the MIN CFM if you will never use MAX...or could be the MAX CFM if you will always run it at MAX. Likely running at the lower CFM setting would result in longer device life. Getting your RH to 30-35% will reduce window condensation issues and moisture/mold issues caused by infiltration. I think all your wood would likely prefer a stable year-round humidity level and resulting moisture content level too.
22 Jul 2020 06:19 PM
We have pretty humid summers. So using an HR to drop the humidity in the winter, while likely a good idea, would create more of a swing in humidity levels over the course of a year.
Do you recommend any brand.of Hrv or Erv? I've been looking at Renewaire and lifebreath
22 Jul 2020 09:25 PM
An ERV won’t reduce your indoor humidity in the winter at all and it won’t reduce it in the summer either when the outdoor air is more humid than the indoor air. If you need to reduce indoor humidity in the summer, you should be looking at AC and perhaps a dehumidifier. Sorry, I don’t recommend brands online. A Google search for reviews and ratings of ERVs or HRVs should get you what you need in that regard.
newbostonconstUser is Offline
23 Jul 2020 03:17 PM
EVR = magic black box = question its effectiveness..... also newer and not much data on how long they last. HVR are simpler and been along in residential longer.
HVR will remove humidity if the outside air is colder then 60 degrees even if the 60 degree air is at 100 percent humidity.
When heating 60 air that is at 100% humidity to 70 degrees the humidity changes to ~50%
So 50 degree air at 100% humidity changes to around ~30% humidity at 70 degrees.
Thus my run of thumb is if the air outside is under 60 degrees it doesn't matter what the humidity is because when it is heated up it will always help keep humidity at or below the safe level of 50%.
thoner7User is Offline
22 Oct 2020 03:31 AM
I'd like to resurrect this old thread because I am also struggling to size a ventilator for my house. I'm in zone 6 and still confused if hrv is better for me.or ERV
I have 2400 sf house with 1600 sf finished basement (4000 sf total). 3 bedrooms, 4 occupants. And 46,800 cubic feet of airspace (which includes basement)
There seems to be 3 ways to calculate the size. ASHRAE 62.2 , the International Building Code, and by cubic feet of house.
Problem is I get wildly different numbers.... Which is right?
ASHRAE = 70 cfm
IBC = 150 cfm
Volume = 232 cfm.
And lastly a contractor who told me 130cfm. Not sure how he calculated that
So what size unit should I get, and what speed setting should I set it at?? Is a u it with 40-100 cfm enough?
22 Oct 2020 05:39 PM
I don’t know that any methodology is “right”… For your design, I get 150 and 70 CFM for the ASHRAE and Building Science methodologies, respectively. But based on your volume number, your average ceiling height is 11.7 feet (i.e., 46,800 CF / 4,000 SF). So I would suggest getting a unit that when it’s operating continuously at its MIN setting will provide about 102 CFM of ventilation capability (i.e., 70 CFM x 11.7 feet / 8 feet). This is equivalent to 0.13 ACH or Air Changes per Hour (i.e., 102 cubic feet/minute x 60 minutes/hour divided by 46,800 cubic feet). And I would place switches in your bathrooms that can place the unit in its MAX setting as needed which will likely provide 150 CFM or more ventilation capability allowing it to meet code. Plan on running the unit on its MIN setting and put the stale air inlets in your bathroom. You may find that running the unit at its INTERMITTENT setting (e.g., 20 minutes ON and 40 minutes OFF) will be adequate too. I don't think I can explain the differences or motivation for getting an EHV or HRV any better than I already did previously.
25 Oct 2020 06:20 PM
Posted By newbostonconst on 23 Jul 2020 03:17 PM
Will an HRV lower your indoor humidity in the winter? In NY?
25 Oct 2020 06:46 PM
I'm getting really frustrated. For the life of me I have no idea how these units are controlled. The only one that seems to have controls is the panasonic intellibalence, with dials right on it to pick your fan speed and adjusting how often it runs.
How do you control the other ones? Other than just min airspeed or max airspeed?? Like if the unit says 40-250 cfm. How do you set it at 90 cfm? Or 130 cfm? Or 180 cfm?
What if the unit is just marketed as 150 cfm? Is that the min or max cfm? Good grief, don't these companies understand that at the end of the day, these units will be in the homes of people without PHDs in HVAC?!?!?!
Smart ShopUser is Offline
25 Oct 2020 08:34 PM
Most home owners are not involved with specifying their HVAC so the manufacturers are marketing to builders and architects.
If you want to know how they work, I would start looking for YouTube videos and also download and read the product manuals.
25 Oct 2020 10:29 PM
Rocket science isn't required, but spending the time to gain a basic understanding is required. These ERV and HRV units typically contain processors and they need to be booted just like a computer and have considerable installation capability and flexibility . These units come with an integrated control within the unit to set speeds and associate desired CFM with these speeds. You can and likely will need to use separate devices/switches to talk to the unit and control it remotely (i.e., switches in your bathrooms). As Smart Shop suggested, I would also suggest reading the installation and user manuals of a typical HRV to gain a basic understanding:
https://s3.amazonaws.com/s3.supplyhouse.com/product_files/Broan-HRV160TE-Install-Instructions.pdf
https://s3.amazonaws.com/s3.supplyhouse.com/product_files/Broan-HRV160TE-User-Guide.pdf
Yes, a HRV will lower indoor humidity in Winter whenever the outdoor temp is less than the indoor temp. An ERV will not.
27 Oct 2020 07:38 PM
So where could I find a "thermostat" type control for these things? All I'm seeing is a button that runs it on Max for 20/40/60 mins.
Thanks for the links to that Broan unit. That's the second one I've found with any type of controls listed in the manual
Unfortunately it's twice the price of all the others and out of stock till winter.
27 Oct 2020 08:12 PM
This pansonic intellibalence is exactly what I need, features wise.
https://www.supplyhouse.com/Panasonic-FV-10VEC2-Intelli-Balance-100-Energy-Recovery-Ventilator-Cold-Climate
I have no idea if it's big enough tho. I looked back at my notes, and I have two companies give me "quotes" for a 130 cfm unit and a 218 cfm unit
So of the 5 different ways to calculate howamy cfm I need, I'm now at 70, 130, 150, 218 and 232.
Should I pick one of those numbers out of thin air? Mean? Median? Mode?!
27 Oct 2020 08:27 PM
I'd really like to buy something already. I've had my windows open all fall and winter. I've done 50 plus house of reading on these silly things. Can anyone just tellw if the 40-100 cfm panasonic unit is enough Ventilation? I can go find my blower door test results if needed.
27 Oct 2020 09:26 PM
I think I am going to get 2 of those or the equivalent for about 1,800 ft^2, or about 18,000 ft^3.
I don't know how those numbers are calculated but one will be for 1-3 people upstairs and one will be for the shop space downstairs.
I will need more ventilation if I am doing TIG welding, plasma cutting or mist spray coolant on my milling machine. I will probably get a straight exhaust fan for that and turn off my shop AC zone when I am doing that. Being shaded by the second story, starting cool and being well ventilated, it shouldn't be too bad even in the summer if I try to work in the morning or after it cools in the evening.
It has been mentioned to have the inlet in the bathroom, I put my inlets right along side and at toilet level. I also have Smartthings automation so I have motion sensors in the bathrooms that turn on the HRV.
The moisture in the bathroom dissipates through the whole room in a ~5 minutes so my runtime after there isn't any motion is 10 minutes.
Has worked great for 3 years. with not moisture problems. I did buy the Fantech 70 cfm version and which pulls under 50 watts at max. Some states regulate there size directly by their current/power they pull. I think the next size up might have been better for smells of some people but it still works.
I have three bathrooms with 4 inch duct to each.
People Online People Online: Visitors Visitors: 328 Members Members: 0 Total Total: 328