Radiant ceiling/floor cooling has been shown to be very effective in hot, non-diurnal temp climates. To remove moisture from the air you either need to expose it to something that is at a lower temp than the dew point or use a material having hygroscopic (desiccant) properties. The new InfoSys building in Hyderabad, India used this radiant cooling approach and a desiccant energy recovery wheel in a DOAS AHU. Half of the building was this radiant cooling approach and the other half was optimized VAV...and this is currently the world's largest HVAC side-by-side comparison. Two years of operation showed that the radiant cooling approach used 34% less energy than the optimized VAV. An interesting "lessons learned" is that the living space dew point had to be kept below the chilled water supply temp, NOT the slab surface temp, in order to avoid having water vapor diffuse through the concrete slab resulting in water condensation within the slab creating a moisture problem. There is a nice write up about it in the May ASHRAE Journal. |