Posted By techlady on 06/25/2009 8:41 PM
What do people think of a radiant barrier, such as Low-E, as a solution here? It could keep some heat out of the attic, and, if you place it over the cellulose, reflect any heat in the attic away from the next floor down.
It depends on how much cellulose is in there in the first place (and how much you might be able to blow in there.)
If you have less than 5.5" of cellulose in there (~R19), then a radiant barrier will give you roughly the "R-equivalent" in cooling of having 11" of cellulose (with negligible improvement in heating-season efficiency.)
If there's space to just blow over to achieve a total depth of 12-15" (R40-R50) that will be more effective than radiant barrier, with significant improvement in the heating season as well.
The performance (and therefore the value) of a radiant barrier is highest when the insulation R values are low. As yo add R-value, the performance of the radiant barrier goes down, since it reduces the total heat by a fixed percentage, and the higher the R-value, the lower the initial heat flux. But the cost never changes. To figure out whether it's cost effective for you to add radiant barrier, based on your R-value & climate, the Oak Ridge National Labs did the math for you already:
http://www.ornl.gov/sci/roofs+walls/radiant/rb_tables.html#table4
Find the R-value & city most similar to yours. The number in the box is the MOST you should pay for radiant barrier (installed) in order for it to at least break-even over 25 years. If you look at the R19 column, you'll note that the maximum cost-effective price per square foot is less than the cost of the material for most cities listed.
They have a similar calc for the cost effectiveness of more insulation:
http://www.ornl.gov/sci/roofs+walls/radiant/rb_tables.html#table6
Cellulose is cheap stuff, and doing open-blow cellulose in attics isn't rocket science as a DIY project. If you have skimpy attic levels it's almost a no-brainer. 25lb bags cost ~$10-11 in big box stores, and that'll cover 40square feet at a settle R-value of ~R19, so that's $025-0.28/ft^2 for the materila. Most of the box-store chains that carry offer a "free rental" of a blower for a coupla days if you buy 10 bags or more.
If you have 4" of insulation or less in the attic it's cost-effective everywhere to add another R19 on top of it. If you already have ~5.5" it's still cost effective to add another R19 as a DIY project in most places- everywhere except Florida & the Gulf Coast and the coastal southern California.
And once you're at R30 or more, adding radiant barrier isn't cost effective anywhere.
So the short answer is: Boost the R-value to R30+ if you can, and forget about radiant barrier. If there really isn't space to go R30+ (rare, but it happens), radiant barrier can still provide some relief at very low R values.There have been literally hundreds of studies on radiant barriers over
the past 30 years at the FSEC and Texas A & M to back up these
guidelines, and the ORNL cost-effectiveness tables are conservative. You might calculate a different price point depending on what you believe energy price inflation will look like over the next quarter-century. But R-value generally trumps radiant barrier, no matter what the price of energy.
The roof is only one part of the solar-gain equation (albeit an important one, particularly on low-angle & flat roofs in southern US latitudes.). Glazing on the E,S, and W sides are another huge factor to control, and exterior shades (awnings or shutters) beat the performance of any low-E coating or window film, etc. (But reflective window film is cheap, and DOES make a difference.)
Another huge factor in older sun-belt studwall buildings is radiant transfer through the siding. Again, exterior shades are more effective than radiant barriers, but light colored paints with infra-red emissivites between 0.3 and 0.6 can make a difference. (But again, not as much difference as blowing insulation into the stud-bay cavites. The cost of retro-insulating walls is much higher than attics per unit R-value, and the solar gains lower, so as a cooling strategy it may be harder to rationalize strictly in dollar terms.)