Posted By randy7652 on 29 Nov 2013 11:02 AM
We have a brick home built in the 50s. It has plaster walls with about a 2" gap between the plaster and brick with no
insulation. I have read all the debates regarding insulating
behind the existing walls. So here is where I need help. Could I build 2x4 walls
over the existing plaster and insulate them and then cover them with
drywall? What would be the steps? Vapor barrier? There is none in the
cavity now. The house is on a slab. I live in northern Indiana where it
is cold and windy in the winter. The exterior walls are very cold to the
touch. I have insulated the attic.
Thanks for any help you can give!
So, the lath is just 2" from the brick, and the brick is the structural wall?
How are the floor & ceiling joists attached?
How deep are the roof overhangs, and how many stories tall?
It's highly likely that you would be able to be pretty safe with an interior studwall approach, and no vapor barrier would be safer than 6-mil poly. Since there is a 2" gap, the brick qualifies as "vented cladding",
in building code terms, and if there is no plywood or plank sheathing, just plaster on lath supported by furring or something, the plaster & lath layer is highly permeable, allowing any interior wall assembly you cook up to dry into the cavity. Most cavity walls are designed to convection-dry, with weep holes at every foot or so along the bottom course of bricks, with the top vented into a vented attic, or sometimes via vent-holes to the exterior. (If it vented into the attic, hopefully you didn't block that when you insulated the attic. But if you did, it can be fixed in a couple of ways. Filling the cavity is not a good idea in your climate, since it carries some rot risk at the joist attachments or , or a high risk of mold/rot in the wooden lath. Keeping it vented cures a lot of ills.
Since the interior studwall isn't structural you have some flexibility in how you build it. To meet code min in your climate (US climate zone 5) you need a "whole wall" R of about R13-R14. You could opt for 2.5" of foil-faced rigid polyiso glued to old plaster wall, secured at each stud with 1x furring through-screwed to the studs 16-24" o.c. on which you can hang blue-board or lath or other interior finish, only giving up ~3.25" of interior space. If you're going for a true high-R performance there is a longer term rationale for as much as 4-4.5" of polyiso (two layers with seams staggered between layers, both sets of seams taped with FSK tape.)
Or, you could put up an inch of polyiso and install a 2x4 studwall 24" o.c. tight to the iso, insulated with blown or damp-sprayed cellulose, or with UNFACED batts. Since it's not structural, single top/bottom plates are fine, as is the wider spacing, which lowers the thermal bridging. With the inch of iso and R15 rock wool (fitted obsessively perfectly) you'd be at about R16-R17 whole-wall, well above the code min, but it eats up about 5" of interior space.
Detail the rigid foam as your primary air barrier- that means caulking/foaming the top and bottom seams, and any plumbing/electrical penetrations, and carefully taping the seams of the facers. Since the foil facers are true vapor barriers, you don't need and absolutely don't WANT and interior side vapor barrier. Air tightness on the gypsum is important, and standard latex paint is sufficiently vapor retardent to not end up with soggy insulation at the foam/fiber layer. The ratio of foam-R to fiber R is important- anything less than R5 at the foam layer and you'd have to dial it back to R11s (or lower) for the cavity fill. Higher-density fiber is more air-retardent against convective loss of performance- anything below R13s would be a performance hit bigger than the labeled R might imply. An inch of foil faced 1.5lb density poly iso is R6-6.5, which is good for cavity fill up to R15 in your climate without interior-side vapor retarders.
Brick walls with stubby roof overhangs are subject to signficant rain wetting, and brick will store quite a bit of that moisture, leading to sustained intense moisture drives when heated up in the sun. The shorter your overhangs, the more important it is to maximize the air flow through that masonry cavity. Foil faced iso would block those drives from getting into an interior studwall cavity, but you still have whatever wooden lath/furring etc in the cavity to keep dry, as well as the joist ends, which need to dry into the cavity, but become susceptible to those hours of steam-heated moisture drive. It's sometimes worth spraying a flash-inch of FrothPak or other closed cell foam on the joists where they penetrate the cavity as an air-seal/vapor retarder, but in a well vented cavity and/or deep roof overhangs you can get away without taking those measures.