The interior heads of multi-splits operate independently, but must share mode- you can't have one head cooling while the other is heating. Both the outdoor & indoor units modulate blower speed, and vary the speed with sensed load. The compressor modulates continuously with load based on feedback information coming back from the heads. When there's no load, the compressors & blowers stop. The loads are continuously sensed via input air temperature(s) at the interior head(s). It's the fact that they are always loping along at part-load that gives them their favorable efficiency, since the coils are sized for the MAXIMUM. In general separate units have slightly higher SEER and HSPF ratings but in practice that's not always meaningful. The most important factors to get right are to size the heads correctly for the zone loads, and the compressor to the maximum load. Most manufacturers will have smaller heads available for multi-zoned units than you can use with even the smallest single. The higher performance ratings for the singles is a matter of optimized algorithms & compressor speeds for serving a single master. When calls are coming in from two heads separately the outdoor unit often plays a hunting game, ramping up, then down slightly, since the loads sensed at the heads really aren't going to be fully sychronized. Cost, and lower standby losses usually favor the multi-split solutions, but not always. In cold/very-cold climates standby losses can be an issue, since each outdoor unit still uses power at idle when it's cold out to keep the compressor and it's lubricants at a non-destructive startup temperature. It's not a huge amount of power, but with multiple oversized units running low duty cycles it can add up. |