Posted By bert seyfarth on 02 Mar 2014 10:12 AM
Under slab insulation helps during heating months but is a detriment during cooling months. I've lived with a copper radiant system without under slab insulation for 30 plus years and have been very happy with the system. Mid Michigan. New systems use plastic instead of copper. Systems using plastic seem to require AC. Will plastic systems work without under slab insul?
The amount of "free" sensible cooling you get from an uninsulated slab is pretty limited, and by letting the slab run at the soil temps you end up with a higher potential for mold growth in the basement during the summer in a mid Michigan location due to the fact that your outdoor summertime outdoor air dew points are well above the deep subsoil temps, and the likely temperature of an uninsulated slab. Any air infiltration/ventilation into the basement ADDS moisture during the summer, and the cool air films at the slab are at or near saturation.
Mold-susceptible materials resting on the slab suffer the inevitable, unless you air condition or mechancally dehumidify the basement. In my case the uninsulated slab costs me on the order of 400-500kwh/year in dehumidification energy use, and in some years it's been as high as 700kwh. My summertime outdoor humidity isn't dramatically higher than MI, though a fraction of the humidity load is from ground moisture, since there isn't a full vapor barrier. Set to control the basement to 60% RH, the humidifier's power use still tracks the weekly average latent load, and goes to near-zero when outdoor dew points are under 55F.