Better to NOT seal the "rim joist area"... in this case?
Last Post 21 Sep 2015 05:12 PM by Dana1. 1 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
djm284User is Offline
New Member
New Member
Send Private Message
Posts:3

--
19 Sep 2015 06:00 PM
I am at the beginning of a DIY adventure of finishing my basement in a small two-story + basement 1940's brick home located in northern VA. The finished product will be a master bedroom and bath, guest room, and unfinished utility area.

My plan is to insulate the brick and block walls in the basement with 2" rigid foam boards and then build the stud wall about 1/2 in front of the foam boards. I may use one of those products that raise the floor up off the concrete slab as well, effectively creating 1/2 in channel under the floor and behind the walls throughout to enable better drying of any moisture that might find its way in. I do not currently have a moisture problem, but its an unsealed 1940's house with no french drain or sump pump, and inevitable a few drops or small puddle will occur sometime in the next 20 years.

What I am debating with myself right now is whether to seal up the "rim joist area" or leave it open for air flow. I use quotes, because there is no rim joist, but I don't know what to call that area. The brick wall extends from the foundation all the way up to the attic. The floor joists extend into the brick wall, so there is not rim joist. With that, there is currently a 1/2 channel between the brick and plaster walls on the 1st and 2nd story. The walls are not insulated, no moisture barrier, etc.

So here are my questions:

1. Am I correct in assuming the air flow created by the open 1/2" channel behind the walls going from the basement to the attic is preventing moisture problems in that area.

2. If yes, and I seal up the "rim joist area", am I risking moisture/mold building up in the 1st and 2nd floor wall cavities, or even at the bottom of the cavity on top of the seal because I will have eliminated that air flow?

3. If yes again, should I just leave it unsealed so air can flow behind all walls in the house, old walls upstairs continuously down to behind new walls in basement (but in front of the rigid foam)?

I've attached a picture to help explain.
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
21 Sep 2015 05:12 PM
To be effective the vented gap has to be between the masonry and foam, not between the foam and the studwall. The foam needs to be tight to the studwall, otherwise the channel is both a thermal bypass, but also a code violation, since  a vertical cavity partly inside the insulaion layer needs fire-blocking to limit fire spread.

The cavity is a capillary break between the moisture-laden brick and the rest of the materials.  2" foam is a fairly good capillary break on it's own, but if the brick can't dry into a vented cavity it's moisture levels remain high, which puts the joist ends in the joist- pockets at higher risk.  The "right" thing to do is to leave a 1" gap between the brick and the foam, and drill weep holes a few inches above grade so that outdoor air can convect into that cavity, and seal the full perimeter of the stud bays to the foam inside of EVERY stud bay, to prevent air migration either sideways or up and down inside the studwall.  If the top of the cavity isn't vented to the exterior, drill vent holes corresponding to the weep holes.  This should be about every third brick or so.




It's generally safe to insulate the brick & joists at the joist pockets with an inch of closed cell polyurethane for a few inches on either side of the joist, using rock wool on the interior of that to fatten out the .   At 1"  the closed cell foam will be ~R6-R7, but would also be about 1-perm of vapor permeance, which allows it to dry toward the interior. It's key to NOT put vapor barriers on the interior side of the studwall anywhere, but even more so in the sections around the joist pockets.

Below grade there's no benefit to the cavity, since there is no way to inject dry exterior air into the bottom of that cavity, which would remain at ~100% relative humidity most of the time.  With the  2" foam tight to the block it has to dry to the above-grade exterior, which it will do just fine.  Concrete block is not adversely affected by moisture but the wood is.  If you maximize the drying capacity of the wall above-grade with a vented cavity properly between the brick & foam  it'll do just fine.

Ideally you would have at least 1' of roof overhang per story of height to limit the direct rain wetting of the brick (?), as well as good surface drainage at grade near the wall, rain gutters to keep the soil near the foundation from becoming super-saturated.

So from outside to inside above grade:

outdoor air | brick | 0.5-1" of air | 2" foam | 2x4 fiber insulated studwall, framing sealed to the foam | interior wallboard ideally air-tight, but no vapor barriers.

The stackup looks like this image scavenged from the web, except that #4  is 2" foam, not reflective insulation (though foil-faced polyiso would give you a slight edge in your application.)




Below grade:

dirt | brick or block | 2" foam | 2x4 fiber insulated studwall, framing sealed to the foam | interior wallboard ideally air-tight, but no vapor barriers.

The below grade stackup on this can be used right up to the first floor subfloor level, or slightly below, provided you make clearances around the joist pockets:






For the ~3-4" either side and top/bottom of the joist pockets:

 brick or block | 1" closed cell spray foam (max) | rock wool or fiberglass batt | vapor permeable interior air barrier  (wallboard is fine)

It's important to make the joist pocket area air-tight to the interior with the closed cell foam, since wintertime air could otherwise come in contact cold enough to adsorb moisture from that air.  If any of the joists appear to be rotting you may have to take remedial measures before insulating.  Making the closed cell foam the condensing surface rather than the cold wood, the moisture content of the joist end will track the moisture content of the brick, which it mostly does anyway, but won't become a higher-moisture area in winter from interior moisture drives.  It may be worth buying a 100-200 board foot 2-part foam kit for this part, depending on how much you are going to do at a time. If it's just small section, a 12 board foot FrothPak (available at most box stores) it probably the "right" solution.