Posted By jlbartley on 26 Oct 2010 01:02 PM
I'm building a home and I have several questions around the exterior walls that I'm wondering if anyone can help with. I live in Zone 6 so I'm in a cold climate area. I'm trying to make choices in building the home that allow for the best energy efficiency at a reasonable cost.
We're considering building:
R19 insulation in the walls
2x6 walls, 16 OC
OSB
1" XPS on outside
Vinyl siding
A couple of questions:
1 - Do we need a housewrap somewhere in here if we have the XPS? Where would be the right place to locate this?
2 - Is 1" of XPS enough? Do we need to worry about moisture issues? I've seen the article listed below that concerns me.
http://www.greenbuildingadvisor.com/blogs/dept/musings/calculating-minimum-thickness-rigid-foam-sheathing
According to this article we need a minimum of R11.25 foam sheathing on 2x6 walls in order to not have condensation in our sheathing or framing.
3 - If I do the 1" of xps and then attach the vinyl siding is this going to cause issues with the siding?
I'd love to hear your thoughts on what we're looking to do here.
Thanks for your time.
The short answers, in order:
1: Housewrap can be used as an air-barrier, drain-plane or both. Tape the seams of the XPS, but don't count on it serving as your primary air-barrier (they SAY they've solved the shrinkage issues over time, but... ) it can go on either side of the XPS, but there are fewer issues if it's not against wooden sheathing, so put it on the exterior of the XPS (they say they've fixed the tannin-degradation issues too, but...)
2: You definitely have to worry about moisture issues in ANY house that uses wood.
1" of XPS IS enough if...
A: You have a 10mm of rainscreen gap behind the siding, between the top with both top & bottom venting (6mm would be enough with vinyl)
B: You use air tight methods on the interior sheet rock (and VERIFY it's integrity with blower door testing.)
C: Use vapor-retardent primer or kraft-faced batts as your interior vapor retarder.
3: Vinyl siding is used on the exterior of foam sheathing all the time, but part A on question 2. Vinyl siding is inherently back-ventilated, but you need to maximize the capacity of the wall to dry toward the exterior if only using 1" of XPS sheathing in your climate zone.
The longer discussion:
What others said about the inadequacy of an ~R23-ish clear wall R-value in zone 6 for new construction. R19 batts typically deliver only R16-17 in the real-world in cold climates, due to the inevitable compressions & voids during installation, and they allow severe amounts of inside-the-insulation convection losses during extreme cold. Blown & sprayed goods do a much better job, since they fill in the available space to near-perfection. At higher density they do even better, since the convection & infiltration losses will drop, and the R-values per inch also go up (to about R3.7-ish for dense-packed cellulose.) Cellulose has the lowest convection & infiltration issues, but noo-skool superfine fiberglass like Certainteed Optima or JM Spider are comparable, but only IF DENSE-PACKED to 1.8lbs/ft^3 or higher. They deliver ~10% more R value than dense-packed cellulose, but unlike cellulose, have no capacity for buffering wintertime moisture accumulation. With cellulose (at any density) using standard-latex and rainscreened siding allows that buffering capacity to work by maximizing drying in both directions, making the assembly more resilient. 5.5" of cellulose is sufficient buffering capacity for zone-6 as long as air-sealing of the interior gypsum is fully up to snuff.
Bear in mind, air tightness (particularly on the interior wall into the wall cavity) is 1000x more important than vapor diffusion when looking at moisture issues. Blower-door testing the shell and fixing all the air-leaks to the exterior prior to insulating the cavities is a worthwhile endeavor, as is blower-door testing the whole space again once the sheet rock & plumbing are all in places. (You may have to sheet-rock the attic prior to the shell test, if it's going to be a vented attic.)
To have enough foam on the exterior to make it a "don't care" situtation for air-leakage condensation in the cavites for zone-6 you'd need roughly half the R to be in foam. with a 2x6 construction that would mean 3" of exterior foil-faced rigid polyisocynaurate aka "iso" instead of XPS (2 layers of 1.5" goods seams FSK taped/caulked), which would yield about R19-R21, then either UNFACED batts (or better, wet-sprayed cellulose) and NO interior vapor barriers, no foil or vinyl wallpapers, only standard latex on the interior wall board. Furring for mounting the vinyl siding would have to be long-screwed to the studs, but you'd have about an R38-R40 clear-wall R-value for a ~10-11" thick wall. This is about the simplest-easiest way of achieving a relatively high-R wall, and it'll have less than half the heat loss of your proposed stackup if you make it air-tight every step of the way.
If you stuck to the R11.25 number as-per the article you'd still have some condensation potential on the sheathing, but it wouldn't be at a damaging level unless there was significant interior-side air leakage. Using cellulose for cavity insulation would take care of that. You can get to R11 with 1-3/4" iso, but use only fiber-faced goods(sold as roofing insulation), not foil faced or you won't have sufficient exterior drying capacity. Alternatively, 3" of unfaced EPS bead board would deliver ~R12, with even better exterior drying characteristics. Combined with wet-sprayed cellulose you'd be in the low R30s range, and highly resilient to wintertime moisture. Here too you'd end up with a ~10-11" wall thickness (just as in the iso case.)
No matter what you do, unless you live in a very high-wind zone 16"o.c. 2x6 is overkill- 24" o.c. will have the same structural capacity of 2x4s 16" o.c. . Reducing the number of studs reduces the thermal bridging, increasing the clear-wall R by about R1.5.