Posted By Sporto on 26 Oct 2011 11:23 PM
I am building a house and am about to have it insulated. My roof is standing seam steel over an ice barrier material adhered directly onto the CDX roof sheathing (i.e. non permeable materials and, therefore, no drying to the exterior). The rafters are 2x12 and I am planning on installing 2" of closed cell foam directly onto the lower side of the CDX although I may want to up this to 3". I understand that I need at least an R value of 10 for the CCF for my home in Seattle (zone 4C) so I may need 3". I have several questions:
1) Should I up it to 3" to ensure no condensing on the inner surface of the CCF or is 2" enough?
2) What material should I use to fill the rest of the rafter bay volume? Previous posts have indicated possibly using wet cellulose but I'm unfamiliar with this material. My insulation contractor is simply recommending a blowing in fiberglass material.
3) Lastly, I'm a bit worried about the presence of the CCF in relation to the in-ceiling canned lighting I've got installed. Should I worry about any possible fire issues of having the heat I would imagine canned lights create in close proximity to the CCF?
Thanks for any helpful advice. I'm probably a week or two away from insulation and want to get it right.
Cheers,
In order:
1: If you go over 2" with most closed cell foam you effectively block drying toward the inteior as well. If you want more than ~ R12 in the foam layer, use a higher-perm closed cell foam such as Icynene MD-R-200 (not MD-
C-200). At R5/inch it's lower R per inch than other closed cell foams but that hardly matters with the thermal bridging of the rafters dominating the heat loss. At 3" (R15) it's rated at 1.3 perms, which is slighly higher than even 1" of most closed cell foam. If you're feeling rich you could go for 6" (R30) and the roof deck could still dry.) Your are correct, according to the IRC, in climate zone 4C (western WA) anything over R10 is adequate for insulating to code min, so 2" of ccSPF (R12) would be OK even if you're exceeding code-min R slightly (which you are), but 3" of MD-R-200 would be somewhat better, since it would have about 2x the drying capacity of generic 2" SPF, and would have fewer condensing hours at the higher-than-code center-cavity R. Cost-wise 3" of the higher-perm closed cell foam is comparable to 2" of generic 2lb foam, but get quotes.
2: If it's a finished ceiling with 1/2" or thicker gypsum board, you can dry blow the fiber behind pre-installed netting (BIBS or Blow In Blanket Systems). Cellulose is preferable to fiberglass in that it will buffer and redistribute any actual condensation that might occur at the face of the foam, eliminating the possibility that it would find it's way into the rafters. If you go with fiberglass, use a new-school product such as Optima or Spider, and blow it to 1.8lbs density to reduce convection within the fiber layer, and a more stable R-value. Specifiy to the contractor that the fiber has to be rolled flat, flush with the rafters, as that will keep the gypsum from being bowed out on day-1 (and with wet-sprayed cellulose or wet-sprayed Spider, pretty much forever.) If cellulose the density isn't as critical- it's sufficiently air-retardent at 1.5lbs open-blow density, but 2.5-3lbs density would be sufficient to keep it from settling even if dry blown in that stackup. If you use wet sprayed products, at 8-10" depths allow at least a week of drying time before closing it in with gypsum, and a month from the time of insulating before painting the gypsum. Keeping the room heated and using dehumidifiers to keep it under 50% RH during the initial drying period is cheap insurance too.
3: Give the foam 3" clearance from the fixture, and use only insulation-contact air tight fixtures. (3" of cellulose qualifies as an ignition barrier for SPF.)
With framing factors included, 2" of ccSPF + 9.25" of cellulose delivers a whole-assembly R of about R36 (or ~R44, center-cavity.) If you used 3" of the mid-density Icynene for fewer condensing hours it changes the whole-assembly R value upwards by about R0.2. If (at significant expense) you did 6" of MD-R-200 and 5.25" of cellulose it only raises the whole-assembly R to ~ R38. This is why putting even a modest amount foam outside the sheathing is a much better deal than putting it between the rafters/studs. R10 outside the sheathing with an all-cellulose cavity fill would be code-legal, and would yield R44 for a WHOLE ASSEMBLY-R (~R49, center-cavity) for similar money.