Posted By NFC on 14 Jun 2012 04:55 PM
Ok, I read it incorrectly. However, with 1x furring, 2" foam and sheathing, 3.5" screws will barely nick the stud.
Presumably the sheathing is already properly nailed to the stud to keep from pulling. As long as the timber screws have at least 3/4" of bite into wood the retention is good enough to handle the loading of the siding, but clearly longer can only be better.
I haven't seen any shorter than 4" anyway (but they may exist), which would give you more than enough. For really thick foam the moment arms get longer and the fastener spacing may need to tighten up if you used a very heavy siding, but for 2" foam you could even get away with 24" o.c. spacing even with stucco or stone, but 16" o.c. gives you a flatter plane to work with at a very marginal uptick in thermal bridging from fasteners. See:
http://www.greenbuildingadvisor.com...athed-wallNot built into the structural specs, (but very real when working with 2lb foam) is the fact that the foam itself adds signficant rigidity to the sheathing, and forms a continuous bond between the furring & sheathing giving it even more structural capacity for carrying the siding.