Posted By Denise1 on 12 Jul 2012 10:35 PM
Once I finalize my insulation plan and see what I come up in the heating/cooling load department I may change my mind. In fact you're probably right.
What I want to know right now is to know if a cedar ceiling with 2" of cc spf under the roof deck plus 15" of dense packed cellulose will stay put or will my boards look like the waves of the ocean. And will 2" be enough to keep the condensing surface out of my cellulose.
4" of EPS sandwiched between two pieces of OSB should permeable enough to allow the upper nailer deck to dry to the interior. Or is it just too much stuff in the stack up and not enough ventilation? The only time I have seen this stack up mentioned was with a furring striped ventilation layer. Maybe that's the only way.
I do seem to be chasing my tail.
I have a hard time reading your stackups in the original post- white space counts...
As I understand your roof stackup is something like :
Metal roof / underlayment or vent gap / nailer OSB / 4" EPS/ strucural roof deck / 2" ccSPF / 15" dense-packed cellulose / MemBrain / 2x cedar
If that's the case you have ~R30 between the metal roof and the interior face of the polyurethane (the condensing surface) and ~R55+ of cellulose between the condensing surface and the interior. Assuming a 40F wintertime dew point for the interior air and a 70F interior temp, the condensing surface doesn't hit the dew point until it's below ~24F outside. If your average January mean temp averages above 24F, you won't need the MemBrain, and in Central Point/Medford
your mean temp is about 39F, which is PLENTY of margin. Yes it gets below 24F every year, but it doesn't dwell below 24F for weeks.
The coldest surface abutting an air-permeable insulation layer (such as cellulose) is where
all of the condensation occurs, because as soon as it hits the dew point of the entrained air in the cavity the moisture begins to deposit there. As the temperature of the condensing surface drops, the dew point of the air in cellulose layer tracks the temp of the condensing surface, but the temperature of the cellulose is above the that dew point. The liquid moisture is concentrated at the cellulose directly in contact with the polyurethane, but since it can wick quite a bit of moisture into it's hollow fiber structures, it won't be wet to the touch or lose R value. Only when it stagnates below the dew point of the interior air for weeks would you end up with anything resembling damp insulation.
The nailer deck can still dry slowly to the interior through 4" of EPS + 2" of ccSPF, but if there's any type of vent gap or air-permeable underlayment for the metal roofing it's capacity to dry to the exterior will be orders of magnitude higher. If the roofing is mounted on 1x or 2x purlins the nailer deck has a HUGE capacity for drying to the exterior.
The cedar ceiling won't warp under the weight/pressure of the cellulose, but it's always a good idea to use fasteners with sufficient pull resistance for the load. At a minimum use ring-shank nails, but screws would be even better, particularly in an earthquake scenario. (But of course those never happen in OR.

)
You might want to cut back to a 1" flash of SPF for cost reasons, saving about a buck a square foot. With a semi-permeable but non-wicking SPF as the condensing surface moisture doesn't condense on/wick-into the roof deck you're trying to protect, and with your winter temps there still won't be enough condensing hours to matter. Replacing the inch with another inch of cellulose means the cellulose layer is now R58, and from the condensing surface out you have about R23, which means it now only has to be below 28F outdoors with 70F interior temp 40F dew point interior air. Even on the very coldest days you would still have some drying-hours, and even on the coldest cold-snap weeks you'd have more drying hours than condensing hours, looking at WeatherSpark data.