I thought the XPS was the better stuff, thanks for more info Dana. Not sure what zone it's considered but I'm in SD. Our builder thinks we're over doing it with putting insulation below our radiant slab so it's good to hear people actually use more. Thanks for the info on the concrete! N
That's why I included the link:
http://tboake.com/carbon-aia/images/climate_zones.jpgMost of SD is in US climate zone 6. In climate zone 6 the long term economics of R10 (even using the more expsesive XPS) is arguable even without the radiant floor, even if you're heating with natural gas. If you're heating with propane/electricity/oil R15 can even be rational on a lifecycle basis. WITH a radiant floor R15 would be the minimum, and R20 isn't insane if heating with a more-expensive energy source. That's 4-5" of EPS, 3-4" of XPS. EPS is typically ~9-10 cents per R per square foot, XPS is usually 12-13 cents. So for rough budgeting figure on $1.50-2.00 per square foot.
For a mid-point on what's economically rational long-term for R-values by climate zone, see table 2 p10 of this document:
www.buildingscience.com/documents/r...mate-zonesNote, those are "whole-assembly" R-values, with the thermal bridging of the structural elements factored in. (eg. A 2x6 studwall with R20 cavity insulation comes in at about R14, not R20, once the R1.2 framing is factored in, and the R of the wallboard, sheathing & siding are added.)
Deep subsoil temps in SD run in the mid-40s F, and while the soil itself has an R value, that value varies a lot by the local soil type and it's moisture content. In addition to saving on heating BTUs, by insulating the slab you will avoid moisture accumulation into the floor from the more humid summertime air, since the slab temp would then track the room temp, not being pulled cooler by losses to the subsoil. The amount it takes for mere moisture protection isn't much- R5 would do it, but it's worth pointing out that added benefit.