Posted By minwiswip on 13 Apr 2014 09:52 AM
Thanks for the reply! I have also looked at those spray foam kits (sans compressor). I have a couple good sized units now for running multiple air tools and the specs I've looked at would indicate they're both suitable.
If I go that route - 1" spray foam behind packed cellulose - what did you use as a barrier on the interior side of the wall? I will be using a variety of interior wall coverings ranging from drywall to old barn boards to tile-over-cement-board. I would prefer to install any insulation I use before putting up any wall covering, of course. Does the temporary insulation install-sheeting to keep the insulation in place (plastic, tyvek, screening) work as a barrier?
Any ideas for the attic space? The ceiling joists are just 2 x 4s. It will be vented on the gable ends and with 'pill boxes' near the ridge. The roof itself is only 6 years old and in good shape for now, but eventually will be replaced with steel and ridge-vented. No option for fascia-area venting as the upper level rooms all have 5' side walls topped with sloped 'roof area' ceilings. Those areas will have to be insulated like the walls.
Again, any help or ideas would be greatly appreciated!
With an an air-imermeable inch (R6) of closed cell foam on the exterior of a 2x4 cavity, and cellulose on the interior side you're looking at R9- R11 of fiber, which is a ratio sufficient to be able to use a class-III vapor retarder (latex paint is OK) on the interior side even for climate zone 7. (Birchwood WI is on the warm edge of zone 7.)
But the interior side needs to be air-tight, and no more than 5 perms.
Since you are using a bunch of different finishes, some of which are impossible to make air tight, the safest bet would be to use a "smart" vapor retarder such as Intello Plus or Certainteed MemBrain detailed as an air barrier between the cellulose and your finish wall. They are class-II vapor retarders when the proximate air is dry (less than 35% RH), but become vapor open when the air is more humid (greater than 40% RH). This characteristic limits the rate of moisture accumulation in the cavity during the cold weather, but allows it to dry rapidly when the assembly warms up in spring, releasing the stored moisture into the entrained air in the cavity.
Of course this approach still works whether you have foam in the cavity or not, and it's fine to use just the amount of foam (or caulk) to air seal the sheathing, which doesn't take much if it's plywood. A full covering of an inch might be called for if it's plank sheathing though.