Fan coils are designed as counter flow heat exchangers, so OF COURSE it makes sense to fix the installation error on all units where they screwed that up! If the system was designed correctly the effects of how the different fan coils on a loop are installed counter flow or not has a negligible (if measurable, with instrumentation) impact on the cooling performance of the other coils. If they are truly in series with the unit below you it'll have a greater impact, but note that the cooling loads of lower floors are lower than that of upper floors, and the duty cycle of the fan in the unit below you will be lower than yours. Only when the fan is blowing would it be delivering warmer water to your coil. When the water is flowing through their coil without the fan blowing it barely changes the water temperature. That's true whether their unit is plumbed correctly or not. If theirs gets re-plumbed to a correct counter flow configuration the duty cycle on their fan will go down. Even though it'll be reducing your cooling capacity a bit while their fan is operating, you'll have more hours of cooler entering water at your coil. If you leave theirs in a non counterflow configuration their fan duty cycle increases, leading to more hours of less-effective cooling from your coil. But as long as the design is correct you'll still get adequate cooling either way. |